    Section Pressure: 105f
    Goodman condenser: GSC130241AE LENNOX furnace: g40uh-24a-045-11 LENNOX Coil: 2.5ton outside tem:106f
    Section Line Temperature :56f. pressure: 105f
    Liquid Line Temperature: 116f Pressure: 275f
    S AIR :59F R AIR: 86F
    does anyone know what's the problem? is it the TXV TOO BIG? or something else?
    NC
    262
    Re: Section Pressure: 105f
    Quote Originally Posted by frankfrank View Post
    27*F delta T......You have extremely low air flow. 400 cfm/ton. Did you take the return and supply directly before and after the coil or did you take it from the vents?
    You need 800 cfm or very close....check your air flow.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Do you mean 105 psig and 275 psig?
    For SI users:
    Suction: 13.3°C, liquid 46.6°C
    Evap.p.: 7.2 bar, cond.p. 19.0 bar
    Assuming R22 refrigerant, 105psig is 63F which is impossible given a suction of 56F
    NC
    262
    If you used the same temp probes for the line sets as you did the return and supply air temps....you maybe have a bad thermometer.