    Just For Fun
    OK one for fun then,this greeted me last week
    the set up:
    two Hitachi ducted splits,one local remote in a staff room,the call was a water leak after work was done to the celling grid
    guess away
    Attached Images Attached Images
    Paul
    "KEEP IT COOL"
  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45
    Re: Just For Fun
    Grilles removed?
  3. #3
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20
    Re: Just For Fun
    Quote Originally Posted by The Viking View Post
    Grilles removed?
    all ducting fine,air off/on grills in place and filters clean
    Paul
    "KEEP IT COOL"
  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45
    Re: Just For Fun
    And it was fully commissioned and running before the ceiling guys were there?
  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20
    Re: Just For Fun
    yep been in years without missing a beat
    Paul
    "KEEP IT COOL"
  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21
    Re: Just For Fun
    It's not an AC, but an Ice machine!
  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21
    Re: Just For Fun
    Quote Originally Posted by superswill View Post
    the set up:
    guess away
    Three points (you choose the order)
    1, You have obviously overclocked the prossesor controling the unit and needed a hugh icebank as a heatsink .
    2, The last engineer left the covers of the comp and electrics so you have used ice to protect it. .
    3, The guy who fitted the vent back on the air ducts forgot to remove the plastic protection thus stopping any airflow
    Yours ever helpfully taz.
  8. #8
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20
    Re: Just For Fun
    Quote Originally Posted by Lowrider View Post
    i stood there for hours with a large gin but nothing came out
    Paul
    "KEEP IT COOL"
  9. #9
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20
    Re: Just For Fun
    Quote Originally Posted by taz24 View Post
    1
    2
    3 all duct fine
    l
    Paul
    "KEEP IT COOL"
  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51
    Re: Just For Fun
    Looking at the pictures, it is obviously either an airflow problem or something not letting the system switch off, or condensate not draining away.
    Air flow problem.
    The ceiling fixers have installed the ceiling just below the grilles thereby blocking airflow causing the evap to ice up and then - well the pictures say it all.
    Not switching off.
    Somehow, the ceiling fixers have prevented the return air reaching the return air thermister, or, trapped a wire, or, etc (I give up)
    Water not draining.
    The condensate drain has been raised out of the way to allow the ceiling to be fitted meaning that the drain pan can't empty. This would cause the indoor coil to sit in water, causing ice formation, which eventually blocks the airflow etc.
    I rest my case your honour.
  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46
    Re: Just For Fun
    Looks like a frozen contactor to me
    Or one of the indoor units turned off.
    Jon
  12. #12
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21
    Re: Just For Fun
    Was the return pipe to the cond unit crimped and causing the gas to flash off from there, thus flooding the suction accum.?
    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa
  13. #13
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    21
    Re: Just For Fun
    ceiling fixers put a screw through interconnect or remote wiring - I've seen this do strange things to a mr. slim in the past.
    Come on give us a clue!
    Andy
  14. #14
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20
    Re: Just For Fun
    Quote Originally Posted by monkey spanners View Post
    Jon
    OK jon,andy and the viking get half a point,
    an indoor unit had been "knocked off" at the local spur during celling work (i admit the spur was the same as the light spurs but still) and the inter connecting cables where crossed from day one being on one remote previous maintenance compies have not seen this (great PPM in place then) causing the indoor fan to stop but the system still too refrigerate,causing one hell of a block of ice above the celling,it was only a energy watching member of staff turning off the local RC one night that cause a small lake the next morning and a call too there new maintenance company (us) to mop it up
    back the what the viking said (i couldn't give a clue that early into the thread sorry mate) it has been like that since installed, being one one remote i guess it was a case of its heating and its cooling so its fine,iam now spending a little longer on every PPM visit clearly marking all indoors and outdoors when doing assist list and not taking existing labeling as Gospel
    Paul
    "KEEP IT COOL"