12-06-2008, 11:48 AM #1
flow rate
How we can increase the ammonia flow rate without using overfeed pump
-
12-06-2008, 11:54 AM #2
Re: flow rate
What are you feeding? What is the current method? High pressure feed, Pumper drum?
-
12-06-2008, 11:56 AM #3
Re: flow rate
now the feeding through surge drum. I want to increase the flow rate by 1.5 :1
-
12-06-2008, 12:09 PM #4
Re: flow rate
How high is the surge drum above the coil? Is the coil not performing properly or have your needs changed?
-
12-06-2008, 12:36 PM #5
Re: flow rate
surge drum bottom is 500 mm above the wet return connection on coil.
-
12-06-2008, 03:20 PM #6
Re: flow rate
Originally Posted by RajkumarIf all else fails, ask for help.
-
13-06-2008, 03:29 AM #7
Re: flow rate
Are you feeding sub-cooled liquid into surge drum, and what is the dry suction outlet relationship ? you are asking for trouble by changing levels in surge drum. Hopefully you have a spare compressor in stock, because you are bound to break something sooner than later. You change system balance and the system will bite you. Generally in the wallet. Iceman chime in around-a-bout now, with your wise and extended experience.
magoo
-
13-06-2008, 04:08 AM #8
Re: flow rate
Originally Posted by magoo
I was hoping to draw out some more comments before I jumped into the fray. There seems to be a misunderstanding of how these systems work.
If this is indeed a gravity flooded evaporator with a surge drum the flow rate is already greater than 1.5:1. At full load the circulating rate is probably around 8 or 10! The higher load creates a lot more gas, so the circulation rate actually increase as the load on the coil increases. It decreases as the load is reduced.If all else fails, ask for help.
Similar Threads
-
flow switch connection
By afeef in forum The Trail of TearsReplies: 18Last Post: 23-12-2009, 06:55 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
high volume flow rate
By cakabo28 in forum Technical DiscussionsReplies: 5Last Post: 04-10-2007, 03:41 AM -
Shell/Tube flow rate?
By reggie in forum FundamentalsReplies: 4Last Post: 17-11-2002, 05:41 PM -
R-134 Chilling Unit
By enginerous in forum IndustrialReplies: 32Last Post: 25-08-2002, 01:12 PM