10-06-2008, 01:23 AM #1
Condensing Unit Above Evaporator
I have to install a free stand split type air conditioner of 48000 BTU/hr and 24000 BTU/hr cassette type in a building where the condensing unit will be
above the evaporator more than 6 m also there will be a
horizontal distance of about 2-3 m out of the evaporator before the pipe go upward to the condensing unit ( Notice : The manufacturer did not say anything
about similar case ) so please advise me with the following :
1- Should I make an oil trap ( at which distance and will it be on the suction or the liquid pipe or both)?.
2- How can I keep the capacity of the unit as high as possible due to this distance?
Thanks
-
10-06-2008, 01:27 PM #2
Re: Condensing Unit Above Evaporator
no matter if the condenser is above the evaporator..
you should take note only in the ff;
-total line set distance
-total rise
-total drop
NOTE: a rise followed by a drop cannot be followed by another rise..
so as a drop followed by a rise cannot be followed by another drop..
its a genral rule to prevent oil migration!With great power Comes Great Responsibility
-
10-06-2008, 03:23 PM #3
Re: Condensing Unit Above Evaporator
Sorry I forgot to say that the cassette units metering devices are capillary tubes ,but I am not sure about the free stand units I will check it later .
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
How to Correctly Size Condensing Unit and Evaporator
By Abe in forum CommercialReplies: 6Last Post: 21-06-2005, 04:26 PM -
Selecting Evaporator coil and condensing unit
By Abe in forum Tools and CalculatorsReplies: 7Last Post: 04-04-2003, 03:20 PM -
Matching Evaporator with Condensing Unit
By Abe in forum Technical DiscussionsReplies: 12Last Post: 25-07-2001, 08:57 AM