Results 1 to 3 of 3
  1. #1
    Join Date
    Apr 2006
    Location
    Libya
    Posts
    18
    Rep Power
    0

    Condensing Unit Above Evaporator



    I have to install a free stand split type air conditioner of 48000 BTU/hr and 24000 BTU/hr cassette type in a building where the condensing unit will be
    above the evaporator more than 6 m also there will be a
    horizontal distance of about 2-3 m out of the evaporator before the pipe go upward to the condensing unit ( Notice : The manufacturer did not say anything
    about similar case ) so please advise me with the following :
    1- Should I make an oil trap ( at which distance and will it be on the suction or the liquid pipe or both)?.
    2- How can I keep the capacity of the unit as high as possible due to this distance?

    Thanks



  2. #2
    Join Date
    Apr 2008
    Location
    philippines
    Posts
    95
    Rep Power
    17

    Re: Condensing Unit Above Evaporator

    no matter if the condenser is above the evaporator..

    you should take note only in the ff;

    -total line set distance
    -total rise
    -total drop

    NOTE: a rise followed by a drop cannot be followed by another rise..

    so as a drop followed by a rise cannot be followed by another drop..

    its a genral rule to prevent oil migration!
    With great power Comes Great Responsibility

  3. #3
    Join Date
    Apr 2006
    Location
    Libya
    Posts
    18
    Rep Power
    0

    Re: Condensing Unit Above Evaporator

    Sorry I forgot to say that the cassette units metering devices are capillary tubes ,but I am not sure about the free stand units I will check it later .

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  3. Replies: 6
    Last Post: 21-06-2005, 04:26 PM
  4. Selecting Evaporator coil and condensing unit
    By Abe in forum Tools and Calculators
    Replies: 7
    Last Post: 04-04-2003, 03:20 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •