    Daikin U4 error code



    Hi fellow members,

    My first post, so please bear with me ...

    I have a Daikin split system with 2 indoor wall-mounted units. One of the units works fine. The other has a flashing green LED when I turn on the power and the error code shows as U4 (Communication error between indoor unit and outdoor EBS unit).

    I am due to call out an engineer, but would like some advice as to potential causes and if possible, some indication of how big a job it would be to fix.

    Many thanks



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Age
    37
    Posts
    12
    Rep Power
    0

    Re: Daikin U4 error code

    Is it as simple as ones in heating ones in cooling mode?

  3. #3
    Join Date
    May 2008
    Location
    London
    Posts
    6
    Rep Power
    0

    Re: Daikin U4 error code

    Hi 4sac,
    I've tried all combinations of temerature, mode, fan speed etc and nothing happens. The vent flaps don't move - nothing. All that happens is the green LED keeps flashing until I switch the whole unit off.

  4. #4
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Daikin U4 error code

    Hi mate is sounds like a indoor pcb fault but i would check the interconnecting wiring first no loose connections etc. its not a big job 2 hours work at the most pcb a couple of hundred pound

  5. #5
    Join Date
    May 2008
    Location
    London
    Posts
    6
    Rep Power
    0

    Re: Daikin U4 error code

    Thanks for the advice. I'll check the wiring first

  6. #6
    Join Date
    Sep 2007
    Location
    IL
    Age
    47
    Posts
    56
    Rep Power
    17

    Re: Daikin U4 error code

    From my experience with those units (we worked only with 4 indoors system) it would probably be outdoor PCB fault. On the outdoor PCB there are 2 communication channels for both of the indoors. You can check on those terminals if they supply similar voltage to both indoors. If the signals are the same, it would be the indoor PCB, if not, outdoor PCB.

    Again, from my experience its an outdoor PCB
    Good luck!
    (tell us later what happened)

  7. #7
    Join Date
    May 2008
    Location
    London
    Posts
    6
    Rep Power
    0

    Re: Daikin U4 error code

    Thanks Krondor. I'll get someoen to take a look in the next few weeks.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin controller
    By mchild in forum Air Conditioning
    Replies: 8
    Last Post: 02-10-2009, 07:14 PM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •