    Cold compressor!!



    Hi guy's..just replaced comp on an isovel DX system, used for cooling a computer room, everything went o.k, comp running, readings on guages suc-75psi diss-250psi, suc line nice and cool diss hot, no blockage in T.E.V or drier, temp of unit great, but whole of comp is v.cold to touch, has been running for aprox three hours, would expect comp to be warm all over by now....Am i worrying about nothing or is there a hidden prob i'm not seeing!!!

    Thanks for any reply's..



  2. #2
    Join Date
    Apr 2005
    Location
    England
    Age
    48
    Posts
    62
    Rep Power
    20

    Re: Cold compressor!!

    Can you tell us the suction supheat?

    I would guess flooding back.

    Sturt.

  3. #3
    Join Date
    Apr 2008
    Location
    Uk
    Posts
    72
    Rep Power
    17

    Re: Cold compressor!!

    Got to agree with Sturt - sounds like liquid flooding back. Probably why the compressor failed in the first place.

  4. #4
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: Cold compressor!!

    Thanks for replies guy's, havent checked super heat today, will check and rectify, will keep you posted if interested.

  5. #5
    Join Date
    Apr 2008
    Location
    Uk
    Posts
    72
    Rep Power
    17

    Smile Re: Cold compressor!!

    Hi - yes would be interested how you get on . What compressor is it and does it have service valves ?

  6. #6
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Cold compressor!!

    Quote Originally Posted by N.Lewis View Post
    but whole of comp is v.cold to touch, has been running for aprox three hours, would expect comp to be warm all over by now...Am i worrying about nothing or is there a hidden prob i'm not seeing!!!
    N.Lewis,

    The first compressor failed for a reason. If you don't find the cause you will loose the new compressor. Seems like you're getting a good sign of the first compressors reason for failure.

    As others have stated, check the superheat.

  7. #7
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Re: Cold compressor!!

    Hi guy's, just to keep you updated, compressor make is compact, and yes it does have service valves, checked superheat, got a reading of 18.5degF, after some adjusting of t.e.v this morning have got that doen to 11degF, comp is now running a little warmer, by the way unit is R22, set point for cooling is 12degC which it is maintaining...Any more info req please let me know...cheers.

  8. #8
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Cold compressor!!

    Airflow on the indoor, air on/off? ducting and filter condition?
    Fan speed/amps in spec?
    Coil and fan blade dust buildup?

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Cold compressor!!

    Quote Originally Posted by N.Lewis View Post
    Hi guy's, just to keep you updated, compressor make is compact, and yes it does have service valves, checked superheat, got a reading of 18.5degF, after some adjusting of t.e.v this morning have got that doen to 11degF, comp is now running a little warmer, by the way unit is R22, set point for cooling is 12degC which it is maintaining...Any more info req please let me know...cheers.
    Your technique of mixing the temperature standards had me going for a while there.

    Are you saying that by reducing the superheat the compressor has warmed up ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Apr 2008
    Location
    Uk
    Posts
    72
    Rep Power
    17

    Re: Cold compressor!!

    Hi- i know its late but- not sure why reducing the superheat would cause the comp to warm up. Surely if anything it will increase the chance of liquid flooding back ? As i say it is late so perhaps it's me !

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Cold compressor!!

    Well that's two of us AH.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: Cold compressor!!

    What is the outdoor DB temperature and Indoor WB temperature. The 75 psi suction and 250 discharge is really close to design conditions. Usually design conditions are 95 degree outdoor and 80 degrees indoor. If you are cooler than design conditions and still holding same suction and discharge psi you are way over charged. Hope this helps.

    Husky






    Quote Originally Posted by N.Lewis View Post
    Hi guy's, just to keep you updated, compressor make is compact, and yes it does have service valves, checked superheat, got a reading of 18.5degF, after some adjusting of t.e.v this morning have got that doen to 11degF, comp is now running a little warmer, by the way unit is R22, set point for cooling is 12degC which it is maintaining...Any more info req please let me know...cheers.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cold compressor!!

    Quote Originally Posted by N.Lewis View Post
    Hi guy's, just to keep you updated, compressor make is compact, and yes it does have service valves, checked superheat, got a reading of 18.5degF, after some adjusting of t.e.v this morning have got that doen to 11degF, comp is now running a little warmer, by the way unit is R22, set point for cooling is 12degC which it is maintaining...Any more info req please let me know...cheers.
    Now, check your subcooling and / liquid sight glass for proper refrigerant charge when conditions are near designed, as well as when conditions are low ambient/low load and high ambient/high load.
    Low ambient and low load check is for ensuring that liquid is not present at compressor inlet in this extreme condition.
    High ambient and high load is for check that you have enough refrigerant for ensuring that TEV has always liquid refrigerant at his inlet at this extreme condition.
    Last edited by nike123; 15-05-2008 at 08:17 AM.

  14. #14
    Join Date
    May 2008
    Location
    Indonesia
    Age
    42
    Posts
    7
    Rep Power
    0

    Question Re: Cold compressor!!

    Low ambient and low load check is for ensuring that liquid is not present at compressor inlet in this extreme condition.
    High ambient and high load is for check that you have enough refrigerant for ensuring that TEV has always liquid refrigerant at his inlet at this extreme condition.[/quote]

    if in the low ambient check he find liquid present at comp inlet then what should he do next..

  15. #15
    Join Date
    May 2008
    Location
    Indonesia
    Age
    42
    Posts
    7
    Rep Power
    0

    Smile computer cooling setpoint

    this morning have got that doen to 11degF, comp is now running a little warmer, by the way unit is R22, set point for cooling is 12degC which it is maintaining...Any more info req please let me know...cheers.[/quote]

    by the way, as far as i know, for computer cooling, the setpoint maintained 18 to 22degC and RH 45 to 50%..its related with the computer reliability..(probably not related with your compressor topic ya. sorry..)

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cold compressor!!

    if in the low ambient check he find liquid present at comp inlet then what should he do next..
    Then he need to take measures to rectify that !
    It could be instalation of suction line heat exchanger to boil that liquid or setting higher static superheat, or installing some suction accumulator.

  17. #17
    Join Date
    Sep 2007
    Location
    England
    Age
    53
    Posts
    55
    Rep Power
    17

    Cool Re: Cold compressor!!

    Hi, just to confirm brian and AH, i was not suggesting adjustment of superheat is the cause for comp heating up, when i posted subject i was just looking for help on the original prob, superheat adjustment was suggested by some of the guy's so that is what i looked at, i thought 18.5degF was rather high as we are always told 4-6 or around 10deg is what we should be looking for (refer to many back posts), so after getting SH down to aprox 11degF comp did warm up?? Anyway system is running o.k so all good.
    Again thanks for all replies..

Similar Threads

  1. Problems with compressor running too cold
    By abrando1 in forum Trouble Shooting
    Replies: 8
    Last Post: 12-05-2009, 10:08 PM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM
  4. Compressor suction icing up on cold room set up
    By Leviathan in forum Trouble Shooting
    Replies: 9
    Last Post: 02-06-2007, 05:08 AM
  5. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •