    Mitsi City Multi 7100 code



    Mistsubishi City Multi system
    Error code 51 7100

    Found this on a system that has recently had a compressor, main PCB and inverter PCB replaced.

    Is this something to do with dip switches on the outdoor unit?

    I'm not really a service engineer I do more of the install side of things so dont laugh at me if its well obvious to you lol.

    Cheers



  2. #2
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    19

    Re: Mitsi City Multi 7100 code

    Hi lonemascot. It sounds like some one has replaced the outdoor pcb and not set it correctly.
    The fault code is system capacity wrong so i am guessing the outdoor pcb is set for wrong size.
    If you look at the reverse side of your units cover the outdoor capacity setting should be there.
    Set it to what ever the size of outdoor it is,
    Hope this helps.

  3. #3
    Join Date
    Feb 2008
    Location
    Basildon, Essex
    Age
    38
    Posts
    11
    Rep Power
    0

    Re: Mitsi City Multi 7100 code

    brilliant, sounds like a most likely cause. Cheers.

  4. #4
    Join Date
    Feb 2008
    Location
    Basildon, Essex
    Age
    38
    Posts
    11
    Rep Power
    0

    Re: Mitsi City Multi 7100 code

    yep just had to set the dip switches.

    until the unit threw a 4210 code. what an absolute mare that was. the transistor modules behind the main PCB had exploded out their sides.

    I now gotta replace those and a diode stack. Dunno if this caused the original compressor failure or vice versa.

    cheers for your help

  5. #5
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsi City Multi 7100 code

    If the compressor windings went with a ground fault this will cause damage to the TRM units in the inverter circuit.
    Some times the inverter board is also damaged so check for ballanced supply to compressor after you have replace the compenents.

Similar Threads

  1. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  2. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM
  3. mitsi city multi r407c
    By mr slim in forum Air Conditioning
    Replies: 6
    Last Post: 06-03-2006, 10:54 PM
  4. Mitsi City Multi Compressor Death
    By aeb200 in forum Air Conditioning
    Replies: 4
    Last Post: 16-11-2005, 09:10 AM
  5. city multi
    By techni in forum Air Conditioning
    Replies: 1
    Last Post: 30-06-2002, 11:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •