    Smile Airconditioning



    1. I AM FACING NEW PROBLEM, THAT IS ONE FRESH AIR UNIT CARRIER MODEL NO.38AH 044-O84 DX. THE GAS LEAK OUT THROUGH CONDENSSOR COIL.
    2. I REMOVED ALL GAS AND BRAZED IT , THEN PRESSURE TEST,(WITH NITROGEN) THEN VACUMMIZED THE UNIT 6 HOURS, (REPLACED DRIER CORE) RECHARGE( GAS22) .
    3. START THE SYSTEM AROUND 30 MINUTS SMOOTHLY RUNNING THEN LIQUID ENTERING THE SYSTEM SUCTION COME TO LOW AROUND 30 PSIG AND TRIPPING ON OIL PRESSURE UNIT SET POINT IS 10 C.
    4. ICE FORMATING AFTER 'TEV ' .



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Airconditioning

    5. Check the TEV, it may be blocked.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Airconditioning

    Quote Originally Posted by V.ARIAN.SHANKAR View Post
    1. I AM FACING NEW PROBLEM, THAT IS ONE FRESH AIR UNIT CARRIER MODEL NO.38AH 044-O84 DX. THE GAS LEAK OUT THROUGH CONDENSSOR COIL.
    2. I REMOVED ALL GAS AND BRAZED IT , THEN PRESSURE TEST,(WITH NITROGEN) THEN VACUMMIZED THE UNIT 6 HOURS, (REPLACED DRIER CORE) RECHARGE( GAS22) .
    3. START THE SYSTEM AROUND 30 MINUTS SMOOTHLY RUNNING THEN LIQUID ENTERING THE SYSTEM SUCTION COME TO LOW AROUND 30 PSIG AND TRIPPING ON OIL PRESSURE UNIT SET POINT IS 10 C.
    4. ICE FORMATING AFTER 'TEV ' .
    Did you used electronic vacuum gauge and did you recharged new or old refrigerant? Try to heat TXV body with hot air (fan) or hot water and look for pressure change. Could be moisture freezing in TXV.

  4. #4
    Join Date
    Apr 2008
    Location
    UNITED ARAB EMIRATES (DUBAI)
    Age
    59
    Posts
    13
    Rep Power
    0

    Smile Airconditioning

    1. i Am Already Replaced The Tev (sporlan E-20)
    2. the Problem Is Still There.
    3. clean Air Filters

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Airconditioning

    Quote Originally Posted by V.ARIAN.SHANKAR View Post
    1. i Am Already Replaced The Tev (sporlan E-20)
    2. the Problem Is Still There.
    3. clean Air Filters
    Please post a replay on question, not new thread every time you answer some question.

    Please, moderators, join this messages in one thread!

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Airconditioning

    Threads Merged now

  7. #7
    Join Date
    Apr 2008
    Location
    UNITED ARAB EMIRATES (DUBAI)
    Age
    59
    Posts
    13
    Rep Power
    0

    Re: Airconditioning

    Finally I got the problem that is after TEV There is distribute lines , Inside this one strainer that is partially block Replaced it now it is working .Thanks to all for your kind co-operation.

Similar Threads

  1. commercial airconditioning
    By faquiambao in forum Refrigeration Books
    Replies: 4
    Last Post: 16-09-2008, 10:18 AM
  2. Engineer Definition
    By botrous in forum Training
    Replies: 26
    Last Post: 14-06-2008, 05:37 AM
  3. Airconditioning
    By V.ARIAN.SHANKAR in forum Air Conditioning
    Replies: 5
    Last Post: 03-05-2008, 10:21 AM
  4. CO2 car airconditioning system
    By liujunwei in forum CO2
    Replies: 5
    Last Post: 17-01-2008, 11:12 AM
  5. Pajero airconditioning
    By Lee G in forum Transport
    Replies: 3
    Last Post: 13-07-2003, 10:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •