    Feb 2007
    SIDE OF THE ROAD
    262
    u9/ue daikin fault
    hi.
    have a problen with a daikin vrv k series system from time to time, i have a u9 being displayed on a central controller with all associated indoors flashing same and a ue on the time schedule,it resets then after a while .. pointers anyone?
    rgrds phil
    Apr 2006
    stafford
    42
    974
    Re: u9/ue daikin fault
    Quote Originally Posted by philjd26 View Post
    hi.
    rgrds phil
    U9:
    system malfunction of tranmission between indoor and outdoor
    systems being switched off at local spur's?
    poor conections of comms wire?
    are a few of the top of my head
    Paul
    "KEEP IT COOL"
    5,667
    Spot on Super
    U9 normally occurs when the outdoor loses comms with one or more of the indoor units.
    Most probable causes are:
    1 - Indoor isolator switched off to one of the fan coils
    2 - Comms wiring taken through the high float limit switch on the cond. pump
    As it's flashing all of the indoors on the central controller, you should look at the indoor ring main power supply and also the 2 core interconnect wiring between the outdoor and the first fan coil.
    The UE fault code indicates a break in the comms between the central controller and the indoor unit.
    Try to trace the wiring or install a temporary 2 core to eliminate the problem
    does the system have any 'add on' pcb's installed?
  1. Daikin fault codes
    By Markie in forum Air Conditioning
    Last Post: 13-01-2009, 01:58 AM
  2. Daikin fault code E6
    By casino in forum Air Conditioning
    Last Post: 24-11-2007, 12:35 PM
  3. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Last Post: 23-07-2007, 01:44 PM
  4. Daikin VRV Fault
    By licencetochill in forum Air Conditioning
    Last Post: 16-06-2007, 08:48 AM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Last Post: 05-02-2007, 02:41 AM