    Compressor Pressures at High Ambient Air



    If you have the following A/C system requirement:

    Continuous operation at 130F Outside Air, 80F Dry Bulb/67F Wet Bulb Indoor Air

    What can you expect your evaporating and condensing temperatures to be?
    I am guessing about 160F condensing and 50F evaporating.

    How would an initial surge of hot ambient air affect the evaporating temperature? In other words, if you started with your return air temp at 130F, would the evaporating temperature be high and how quickly would it come under control?

    How much higher would a blocked filter drive the condensing and evaporating temperatures at this high ambient condition?

    - Andreas



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Pressures at High Ambient Air

    Quote Originally Posted by Andreas11 View Post
    If you have the following A/C system requirement:

    Continuous operation at 130F Outside Air, 80F Dry Bulb/67F Wet Bulb Indoor Air

    What can you expect your evaporating and condensing temperatures to be?
    I am guessing about 160F condensing and 50F evaporating.

    How would an initial surge of hot ambient air affect the evaporating temperature? In other words, if you started with your return air temp at 130F, would the evaporating temperature be high and how quickly would it come under control?

    How much higher would a blocked filter drive the condensing and evaporating temperatures at this high ambient condition?

    - Andreas
    The evaporating and condensing temperatures are dependent upon relative coil sizing and surface area, as well as temperature and volume of airflow.

    Why do you ask?

  3. #3
    Join Date
    Jan 2008
    Location
    Ohio
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    We make air conditioning systems for locomotives. The system is contained in one box, like a large scale window A/C unit. We are trying to get a rough idea of the compressor amp draw at that high ambient air condition, 130F, to size our electronics. I am trying to make the connection from the high air temperature to the compressor suction and discharge pressures. There is also the concern of the blocked filter and how this would drive up compressor pressures. In addition, we wonder what would happen initially if the locomotive cab is also at 130F.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Pressures at High Ambient Air

    I assume you are referring to a blocked refrigerant filter/drier, not a blocked air filter?

  5. #5
    Join Date
    Jan 2008
    Location
    Ohio
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    dirty condenser filter is what I meant

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Pressures at High Ambient Air

    That's still not clear. Are we talking about an air filter or a refrigerant filter? (Yes, there is such a thing as a condenser air filter)

  7. #7
    Join Date
    Jan 2008
    Location
    Ohio
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    condenser air filter

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Pressures at High Ambient Air

    Condensing temperature runs 20-35F over ambient, depending upon condenser size and airflow. Any blockage of airflow, such as a blocked condenser air filter, will add to this.

    The low side pressure can be limited by MOP charge in the TXV and/or a CPR valve.

    You might want to reconsider switching to R410A. At those temperatures, the pressures are going to be horrendous. You will need heavy duty everything.
    Last edited by Gary; 27-03-2008 at 10:05 PM.

  9. #9
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    Hello all
    do you think that using R134A for that application is way off also just thinking ? if not why not ? thanks
    He who does nothing does nothing wrong !

  10. #10
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Compressor Pressures at High Ambient Air

    r134a wouldn't be bad, there's a reason why they use it in cars, high ambients and load, and the fact that you don't need a low evap temp for a/c.
    wait: who even mentioned the refrigerant, I re-read the post and the OP didn't even mention it.
    Last edited by paul_h; 28-03-2008 at 12:00 PM.

  11. #11
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    thanks paul does that mean i get a brownie points im sure other with say im wrong
    He who does nothing does nothing wrong !

  12. #12
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    hello all i know he didnt mention the type of gas but gary said you would be better of using r410a for that application but i was thinking r134a would be better for that application as you said we use it in cars high temps and heat loads
    cheers
    declan ps im bored in madrid with no work
    He who does nothing does nothing wrong !

  13. #13
    Join Date
    Jan 2008
    Location
    Ohio
    Age
    55
    Posts
    10
    Rep Power
    0

    Re: Compressor Pressures at High Ambient Air

    Thanks for the information, especially to Gary. The refrigerant is 134a.

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor Pressures at High Ambient Air

    Quote Originally Posted by paul_h View Post
    r134a wouldn't be bad, there's a reason why they use it in cars, high ambients and load, and the fact that you don't need a low evap temp for a/c.
    wait: who even mentioned the refrigerant, I re-read the post and the OP didn't even mention it.
    The OP discussed switching refrigerants from R134a to R410A in another thread. I would strongly advise against using R410A in this application.

  15. #15
    nairb02's Avatar
    nairb02 Guest

    Arrow Question : How to post a new one here..

    plz help me i dont know how to post in forums.. im a newbie here so please help me. i have lots of questions to ask thats why i want to know how to post in forums.

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Question : How to post a new one here..

    Quote Originally Posted by nairb02 View Post
    plz help me i dont know how to post in forums.. im a newbie here so please help me. i have lots of questions to ask thats why i want to know how to post in forums.
    And, you are just posted, as you see.
    Go to forum relevant to your subject:
    http://www.refrigeration-engineer.com/forums/index.php
    And hit New Thread button on top of opened page.

  17. #17
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Compressor Pressures at High Ambient Air

    Read this forum.
    http://www.refrigeration-engineer.co...splay.php?f=25

    And specifically this post I wrote about basic navigation

    http://www.refrigeration-engineer.co...77&postcount=2

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Air Cooled Mono Block Units & high Ambient
    By smpsmp45 in forum Technical Discussions
    Replies: 4
    Last Post: 11-12-2007, 06:29 AM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  5. Head Pressure: How High is Too High?
    By HHC in forum Fundamentals
    Replies: 7
    Last Post: 15-07-2006, 05:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •