11-04-2008, 08:57 PM #11
Re: TXV's To Adjust or Not to Adjust - That is ....
What happens if the evaporator fans stop working? The orifice is effectively oversized and so the valve will hunt and may cause premature failure of the compressor due to liquid hammer.
I have to disagree The orifice is not oversized it is the same size and the t.e.v will close down via the bulb sensor, and if it has not been ADJUSTED incorrectly liquid should not reach the compressor as the valve is shut down .System will cut out on LP control. No damage done.