    Problems with a Blue Box HP

    Tuesday, I visited a HP air/air monobloc.


    Scroll Manuerop inside SZ090 on R407c, 3 phase.
    Started up in heating mode: 3,3 bar LP (45 psi), 24.5 bar HP (355 psi)
    Outside temperature 11.3°C (52°F)
    Discharge temperature: 111°C, (232 °F) liquid 46.5 °C (116°F) suction right after the evaporator was 7°C (44.6°F)
    Turbine Nicotra over the condensor 12/9.

    Measured airvolume over condensor 2.400 m³/u (1413 cfm)

    Opened valve till SH of +/- 7K
    3.6 bar (52 psi) / 26.2 bar (380 psi) discharge 96 °C (205°F), liquid 53°C (128°F)

    The unit works with a bad COP.

    This machine is a replacement for a Carrier 50HS060

    Inside is a liquid receiver without valves. I suppose both tubes are going to the bottom of the receiver. Otherise, I do'nt see how they circulate the liquid when reversing.

    Complaints: client monitored power consumption since 1999 with the Carrier which was allways around 32000 kWh/year. Now this is increased to 43000 kWh/year.

    When the units was just started, he had to reset the HP once a day, seems that this happened mostly after a defrost?
    There's no suction accumulator.

    Most important complaint is that during the coldest days, it took hours and hours to raise the temperature from 19°C to 20°C (66.2°F--> 68°F)
    Reaching 22°C (71.6 °F) inside wasn't possibel when it was -3°C (26.6°F) outside.
    The old Carrier HP could reach easily 25°C (77°F ) inside.

    The old ductwork is still the same and in very good condition.
    The ductwork is made of PU plates (alu foil inside) of 4 cm thick.

    The suction on the condensor leaves the coil on the upper side of the coil. This seems strange for me...what about proper oil return?

    Comments please .
    NoNickName!
    Last edited by Peter_1; 14-12-2006 at 07:19 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  2. what's the problem
    By botrous in forum Air Conditioning
    Replies: 35
    Last Post: 22-06-2008, 02:54 AM
  3. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  4. Condensation Problem At Door to Freezers
    By mmarch in forum Air Conditioning
    Replies: 5
    Last Post: 17-10-2005, 02:42 PM
  5. Problem with centrif - help requested
    By Brian_UK in forum Industrial Compressors
    Replies: 5
    Last Post: 03-08-2005, 10:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •