    Pipe Sizing on Multiple Evaporators

    Hi Guys - New member, please go easy on me

    I'm doing something a little bit different; I've installed similar systems, but now working for a new employer have been asked to both design and install.

    So it's going to be a 150kw cold room; setup will be 2x 75kw systems with 5x 15kw evaporators for each unit. 5C room temp, 10k superheat, TEV & magnetic valve (each with its own controller) on each evaporator & inverter controlled condensing units to control the required load. Total Piperun 35m, and will have an 8m lift (condenser will be lower)

    I have a rough idea based on my training and literature online to judge I need 2.1/8" Suction & 7/8" Liquid, and is also the connection coming off the condensers (coincidental), but how do I determine the pipe sizes that lead to each/ evaporator?

    So, I'm expecting to use 15kw for my calculation, which gives me 3/4" & 1/2" pipework. Does this sound about right?

    Any help is much appreciated