15-03-2017, 10:03 AM #1
Church A/C
Hi Guy's,
Need some advice on installing A/C in a Church.
My calculations work out to 33kw of A/C required for this given job.
This is fine, I can put 2 10KW splits at each end of the building.
My Problem comes in on Heating. As you all know hot air rises.
Church has a 10m ceiling. The lowest point I can put the indoor unit is 3.5-4m high.
I'm worried that the units willl cut out on t/stat before the lower area of the church is actually warm.
Maybe I can source a remote temp sensor and mount it at 2m below the indoor units?
But will the units be running non-stop to heat the desired occupied area?
Thanks,
Keza