Just looking for opinions on problems with a 2 door commercial freezer with temps in Celsius.
Temperature 0° and rising.

Suction line P/T at service port 5.7bar/3°
Suction line at evap outlet 4°
Compressor discharge pipe 2 inch from pot 126°
Liquid line at condenser outlet 33°
Condenser inlet 83°
Air on condenser 29°
Air off condenser 36°.
Compressor amperage - 7amps.

There's no service port to get high side gauge reading.