04-11-2010, 10:00 PM #11
Re: New system tripping on low pressure??
I just noticed your post. You are probably right.
The subcool will increase as the ambient rises to design. It usually then decreases again when ambient exceeds design.
The superheat is high because the head pressure is too low but the superheat is also not so high because the evaporator air on temperature is also low. Raise the head pressure to design levels and we will see the superheat crash. This would confirm a low load condition which would be either because of low air flows or low air temperatures or both.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Max low side pressure in R404A system
By Wilade in forum Technical DiscussionsReplies: 8Last Post: 25-08-2009, 09:23 PM -
Low Pressure tripping
By Beginner in forum Trouble ShootingReplies: 16Last Post: 18-05-2008, 05:21 PM -
Fan model for system optimization
By autt in forum System OptimizationReplies: 8Last Post: 31-03-2007, 05:34 AM -
Liquid Overfeed Systems
By US Iceman in forum NH3Replies: 151Last Post: 08-03-2007, 05:34 AM