    Daikin RY71FJ7V1 Fault

    I was called out to an R22 Daikin unit with E3 high pressure fault compressor keeps tripping within a couple of seconds.
    The unit was reinstalled by a company a couple of weeks ago they have told the customer its nothing to do with there installation work. when i put the gauges on there is no sign of any refrigerant on either the gas or liquid valves, i rang daikin and they were as baffled as me and said it must have a mager leak which that may be the case i will be going back with a bottle of OFN, but if this is the case why is it showing high pressure fault.

    Also have a look at what I found when I went to the outdoor units 12" between the fans facing each other and insulation missing on some pipe work apparently all of these units have just been reinstalled.
    Attached Images Attached Images