05-01-2009, 05:39 PM #1
Mitsubishi Electric Intermittent fault
Over the weekend one of the guys on call was sent to look at an aircon problem at a restaurant. He looked at the controller and found it flashing P8 02, he reset the fault and i was sent up there today to try and figure out the problem.
As i arrived on site i found 9 indoor units and 5 controllers, i worked out that there were 4 twins and one single split.
The indoors were all running as were the condensors. I found the P8 was an abnormal pipe temperature fault. I would normally associate this with a possibility of lack of refrigerant so i put the indoors on cooling and then heating and they worked fine.
I checked for cross wiring but everything seemed in order.
I then checked the resistance of TH1 TH2 and TH5 which were the return air sensor, Liquid line pipe temp and evap temperature of both units and they were all fine.
I rang mitsubishi up and they seemed to be going down the route that they could be undersized something which i can't beleive.
Has anyone come across a P8 fault on the new Mitsi Electrics?
The model number indoor PLA-RP125BA
outdoor is a PUHZRP250YHA2The difference between genius and stupidity is that genius has its limits.
Marc
Similar Threads
-
mitsubishi heavy split fault
By grovecoooling in forum Air ConditioningReplies: 7Last Post: 13-03-2011, 12:29 PM -
Mitsubishi Fault codes
By steptoe111 in forum Air ConditioningReplies: 6Last Post: 15-12-2009, 02:25 PM -
Mitsubishi Electric VRF help
By marc5180 in forum Air ConditioningReplies: 10Last Post: 04-11-2008, 09:40 AM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 10:23 PM