Thread: Infiltration Cooling Load?
Threaded View
-
13-12-2008, 04:11 PM #1
Infiltration Cooling Load?
Hi all, I have a school project and I need to calculate the overall cooling load of a given office building. I already calculated the exterior and interior cooling loads, however when I calculate the infiltration load I find q to be well over 100000 Btu/hr. and that cant be right.
So here is what I have. 0.5ACH from 8am to 6pm, and 0.2 ACH the rest of the time. The site is Denver Colorado in July. I have been using the formula
q=4840(cfm)(deltaW). From the Psychrometric charts I found the indoor W=0.0122, and the outdoor W=0.029. so the difference or delta W = 0.0168. And I get a value for unoccupied + occupied = 6830.21Btu/hr.
my total cooling load was calculated to be 36015.09Btu/hr. This factors in people, appliances, radiation, and heat transfer through the walls and roof.
I understand there is alot more you need to know before you can give me the exact answer, however a ball park estimate would work.
First of all does this sound relatively close? and is there some other factor I am overlooking??
any help would be appreciated
Rankin755
UW-Milwaukee
Mechanical Engineering
Similar Threads
-
Cooling load calculation
By naveenvm in forum FundamentalsReplies: 19Last Post: 22-07-2011, 05:44 PM -
Cooling Load Calculations
By hamidpia in forum Tools and CalculatorsReplies: 7Last Post: 05-02-2009, 08:57 PM -
Heat transfer coefficient - Coolpack
By Graham in forum FundamentalsReplies: 10Last Post: 28-05-2008, 01:08 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Cooling Load Calculation
By jervame_sireh in forum FundamentalsReplies: 0Last Post: 21-04-2007, 11:05 PM