    Faulty transformer and condensate pump on Daikin split

    Hello everybody!

    Came accross a faulty internal condensate pump on an old Daikin R22 cassette (A3 fault code) and changed it for a new one. System then came up with an E0 fault code (protection device) and having checked the outdoor unit found faulty 240 - 24v transformer for the control circuit / PCB.

    I am assuming the transformer was holding off one of the magnetic relays on the PCB therefore the E0 fault and presume this was co-incidental with the faulty pump on the indoor unit?

    Outdoor unit R60F7V1 R22

    Kind Regards

    Contactor
    Last edited by Contactor; 11-04-2008 at 08:57 PM.