26-06-2006, 06:31 PM #1
Elliwell digital controller
Hi all,
i've running 5 control switch board each controlled with elliwell 974 digital controller for respective cold room, it often problems occurs with elliwell 974 (probe problem, timing problem, setting running problems etc...), any alternative for the above digital controller or any technical advise.
Thanks.
p/s: no problems with Main current supply & refrigeration systems...
-
26-06-2006, 06:34 PM #2
Re: Elliwell digital controller
We installed at least hundred Eliwells (mostly 974) the last years and never experienced any problems with it.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
26-06-2006, 08:03 PM #3
Re: Elliwell digital controller
Only problems we've had are with the 240 volt models the 12 volt range is fantastic
-
27-06-2006, 09:28 AM #4
Re: Elliwell digital controller
eliwell is good, but if you want some other brand try Dixell
-
27-06-2006, 07:48 PM #5
Re: Elliwell digital controller
elliwells are probley one the best available,most problems are understanding and setting the parameters,once you have done a few there easey and very reliable,only things to watch are---dont swich any load exept controlls as the relays are small,allways have the end of the probe faceing upward to stop water ingress and i allways site it inside the end panel,valve side on the top run of the coil loop,that way its at the coldest point and stops any ice formation, good units.
-
29-06-2006, 03:04 PM #6
Re: Elliwell digital controller
=dont swich any load exept controlls as the relays are small,allways have the end of the probe faceing upward to stop water ingress and i allways site it inside the end panel,valve side on the top run of the coil loop,that way its at the coldest point and stops any ice formation, good units.Last edited by Peter_1; 02-09-2006 at 02:50 PM.
-
02-09-2006, 12:46 PM #7
Re: Elliwell digital controller
well i have the two probes are high temp and when the unit is on it rises im using id 974 ,have you ever come across this problem buddy ,100 fitted you must have had a sniffle??
-
02-09-2006, 02:55 PM #8
Re: Elliwell digital controller
Switch parameter H00 in the CnF section from 1 to 0 or vice-versa and very important... because this isn't mentioned in any manual, switch then the power on and off for some seconds.
Only then the new programming will take affect.
Your device is now programmed for the wrong probe (a PTC instead of an NTC or vice-versa)It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
12-09-2006, 12:38 PM #9
Re: Elliwell digital controller
-
06-11-2006, 09:45 AM #10
Re: Elliwell digital controller
for what its worth, i find the carel ir33 range of controllers fairly good, followed by the dixel xr range - i have personally only installed a few elliwell controlers (when local suppliers had none of the others), once you get how to program it up they too work quite well.
"Old fridgies never die, they just run out of gas!"
-
07-11-2006, 07:08 AM #11
-
25-09-2009, 06:57 AM #12
-
25-09-2009, 11:36 AM #13
Re: Elliwell digital controller
hi all i go along with peter1 we have installed hundreds of these ID974 controles with almost no problemes
we however do not connect loads directely to the device but use control relayes as mentioned by" old gas"
Similar Threads
-
Micro-cool controller
By bernard in forum Supermarket RefrigerationReplies: 6Last Post: 25-08-2006, 07:10 AM -
dakin controller
By mike live in forum Air ConditioningReplies: 5Last Post: 27-06-2006, 08:12 PM -
Help with new electronic refrigerator controller !
By EngiGal in forum New TechnologiesReplies: 17Last Post: 08-04-2006, 07:39 PM -
Controller wiring
By Mickvee in forum Air ConditioningReplies: 2Last Post: 30-12-2005, 02:04 AM -
Fan Controller
By Abe in forum Trouble ShootingReplies: 4Last Post: 12-01-2002, 02:21 AM