    Grease instead of OIl in Daikin compressor
    No traces of moisture ..opened after a failure and found grease-like content in the compressor instead of oil.
    Anyone an idea of what this can cause?
    5,667
    Re: Grease instead of OIl in Daikin compressor
    Hi peter
    Is the system on R407C?
    Oct 2003
    5,630
    Apr 2008
    58
    47
    Is this off a VRV system?
    Jul 2006
    865
    Could this be analysed in a lab like an oil sample?
    Oct 2003
    5,630
    Quote Originally Posted by NH3LVR View Post
    That's what I also suggested...it's coming out of a VRV system... anyhow, very strange... and interesting to know the cause, also for the Daikin factory... it"s someone working for the factory here nearby asking me this
    5,667
    I've seen something similar on many R407C systems where poor installation practices had been carried out - basically insufficient vacuum leading to moisture in the system.
    Not seen anything like this on R410a systems though.
    Dec 2010
    devon
    837
    Had some similar oil breakdown with contaminates causing excess heat in comp both times eev stuck causing bypass straigh back to comp
    ireland
    1,453
    Interesting post on linkedin earlier from a motor rewind company, if the shaft of an inverter motor isn't grounded properly then current can flow through bearing to ground, via the oil/grease, does it effectively cook it i wonder?
    Sep 2003
    ISRAEL
    72
    4,248
    Looks like moisture in the system.
    Bring the lab results please.
    Oct 2003
    5,630
    Thanks so far for the input, I'l keep update as soon I have more news... They replaced compressor and it was a tech whom was curious what was inside the compressor... they were in fact not very interested in the cause of this problem... but Daikin can leaer na lot of such a problems
    3,853
    Don't think its was due to moisture as I would expect there to be copper plating on the bearing surfaces if moisture levels were high.
    Have seen oil turn black where discharge temperatures are high, either due to leaking valve plate in a recip comp, and also once where someone had fitted a 3.5kw indoor unit on a 5kw outdoor, suspect it cooked itself in heating mode, the discharge pipe was full of similar black contaminant. Maybe its ran with air in the system due to incorrect vacuuming procedures?
    Wouldn't want to warranty the replacement compressor!