Results 1 to 10 of 10
    Jan 2012
    Namibia
    5
    Cool carrier compressor problems
    Hi everyone
    I'm new to this site but from what ive read so far it sounds like you guys know your stuff. Ive got a carrier reefer(69NT40-511-312) with a recipient compressor that stays in a vacuum and doesnt reach its set point, i think it mite be the txv that is faulty but any other advise would be greatly appreciated.
    Set Point -20
    Return temp -0.2
    Supply Temp -16,7
    SMV 100% Open
    Thanks in advance
    -20
    Melbourne
    347
    Re: carrier compressor problems
    no air flow, so blocked evaporator coil or fan clutch not working so no drive to fan in back, try these first.
    if you take off the evaporator panel you'll see a big ice formation
    Nov 2009
    Canada
    123
    have you physically check the SMV may say100% but could be stuck closed
    Melbourne
    347
    he has a very big temp difference across the coil, so i'm thinking simple stuff first
    Jan 2012
    Namibia
    5
    thanks for input guys, but after further investigation i found that the txv bulb was broken. replaced faulty part, reefer running fine now.
    Anybody know where i can download th new 5#54 carrier software, the port i work at is not a registered carrier service centre so i cant get the software from carriers site?
    May 2006
    India
    399
    I work with a compressor manufacturing company............... Anytime anything goes wrong other than with compressor , customers relate it to compressor faulty , not working ,defective etc . I thought it is a local phenomena but appears to be a common .
    Jan 2012
    Namibia
    5
    No guy, like i said the TXV was faulty. Nothing wrong with the compressor, i wasnt even hinting at that...
    Dec 2010
    Philippines
    33
    30
    me me me me i have problem the suction section of my compressor is icing heavier and heavier as time past when the unit is running what is the probable cause of this????
    Dec 2010
    Philippines
    33
    30
    Melbourne
    347
    Quote Originally Posted by -20 View Post
    rom the threa
    apart from the thread title..