Results 1 to 4 of 4
-
10-01-2009, 05:23 AM #1
subcooling and superheat are standard measurement or not?
Hi, Everyone, I'm working on a research for centrifugal chillers. I want to make an investigation whether 'subcooling' and 'suction superheat' are standard measurements for different brands of centrifugal chillers(McQuay,Trane,Carrier,York). For McQuay, subcooling and superheat are standard measurements. For, Carrier, they don't measure subcooling and suction superheat. I am not sure whether they are standard for other brands of chillers or not. In addition, can anybody provide rating data(performance data) of different brands of chiller.
-
10-01-2009, 07:05 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: subcooling and superheat are standard measurement or not?
What you mean by standard measurements? You can not make correct evaluation of chiller performance without these two measurements (among others).
Doesn't mater what is brand name.
If you mean does the chiller itself take these measurements and record or show on display, that is only question on installing two pressure and two temperature sensors and some interface for recording and displaying these measurements.
-
10-01-2009, 07:19 AM #3
Re: subcooling and superheat are standard measurement or not?
-
10-01-2009, 11:39 PM #4
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Help on superheat and subcooling
By hvac student in forum Trouble ShootingReplies: 8Last Post: 08-08-2008, 02:25 PM -
Subcooling at TEV vs Superheat at Compressor relation in Steady State
By GXMPLX in forum FundamentalsReplies: 12Last Post: 14-07-2008, 03:00 PM -
Superheat and subcooling
By marc5180 in forum TrainingReplies: 27Last Post: 08-10-2007, 09:21 PM -
Subcooling & Refrigerants
By US Iceman in forum FundamentalsReplies: 40Last Post: 29-04-2006, 02:59 AM