Results 1 to 11 of 11
    India
    688
    Temperature pull down in large cold stores( -25 deg c)
    We are following a system of temperature pull down for large cold stores at the stage of commissioning. What are member's views / experience on that method. May be we may need to fine tune our method
    Jan 2006
    Croatia
    68
    2,261
    31
    Re: Temperature pull down in large cold stores( -25 deg c)
    Hi, smpsmp45
    Quote Originally Posted by smpsmp45 View Post
    Please can you tell us your method, in detail?
    Best regards, Josip
    Mar 2005
    638
    Are you talking about coolers or freezers?
    Ken
    India
    688
    It is -25 deg c & hence it freezer. I shall send what we are doing for this pull down. The files are over 200 KB & hence it is difficult to post those here. I shall try & reduce the size if possible.
    Nov 2006
    63
    392
    In reality yo should be looking at a minimum of 14 days pull down may be longer if you have a concrete floor, if not you will damage the floor. I did a store several years ago and due to external control problems we took three goes at it as every time we got so far through the sequence somebody shut the plant down remotely and the temperature went to high.
    Ian
    Mar 2005
    638
    Like noted above, you need an extended pul down in a freezer. You need to pull it down to about 33 to 34 dF (1 or 2 dC) and hold it there fro several days and give it a chance to dry the place out. Lots of moisture in the wals and slab. Them you want to drop it slightly below freezing and hold it there. Continue on down in stages and give the room time to equalize.
    If you rush it, you stand a chance of buckling the floors.
    I had one large cooler in Houston the we tried to pull down in August. It took it the better part of 4 weeks to dry the place out to the point we could pull on down to 35 dF room. The coils had water literally pouring off the pans.
    Ken
    Oct 2005
    IRAN
    878
    Hi there,
    Have a look at the http://www.refrigeration-engineer.co...ead.php?t=8394 post #6 (attached file).
    Even Einstein Asked Questions
    India
    688
    Many thanks
    Mar 2006
    dallas, texas
    75
    108
    I have seen schedules that limit your pulldown in many ways with freezers we have built. But, I agree with Tx Ice that taking the freezer to 35 to 36 degrees f relatively quickly works well, then holding there till no more moisture comes out of the evaporator drains. This may be 4 days or 20 days This is the important point. Once the drains do not flow any more then you can proceed to go below freezing at approx 5 to 7 degrees per day . This has worked without fail for over 20 years of construction on freezers of all sizes.
    Best of luck
    Sep 2006
    Venezuela
    259
    One important point when you pull down the temperature is to keep the door ajar. This evoid to have vacuon inside the frezer
    Oct 2007
    AUCKLAND
    43
    7
    Thumbs up Re: Temperature pull down in large cold stores( -25 deg c)
    hi mate
    just commissioned a large -25 store
    set to +5c for a week or until coils stop freezing over (leave suction pressure as for operation)
    set 0c and drop by 2 -5c every few days will be fine
    make sure underfloor heating all ok
  1. Structural columns in the cold stores
    By smpsmp45 in forum New to RE
    Last Post: 06-10-2007, 11:42 PM
  2. Multiple ref. units for cold stores
    By smpsmp45 in forum Commissioning
    Last Post: 21-06-2007, 06:02 PM
  3. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Last Post: 19-03-2006, 01:43 PM
  4. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Last Post: 16-11-2005, 11:23 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Last Post: 20-05-2003, 12:27 AM