    retro fit r22 to r410a



    hi,would it be ok to use exsisting piework from r22 to r410a provided i flush pipework?

    rgrds phil



  2. #2
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: retro fit r22 to r410a

    Hi Phil

    Are there some problems involved in replacing the pipework?
    I have flushed lots of pipe in the past for various reasons and allways used endoflush, allthough not as good as the old R11.
    It would be good practice to replace if possible.

    Regards

    PP

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: retro fit r22 to r410a

    Hi Phil,
    R-410A’s pressures are about 50% higher than R-22. That's why R-410A cannot be used as a retrofit fluid in R-22 equipment. This is also true for pressure gauges, recovery tanks, recycling units, disposable cylinders, etc. A better solution to retrofit for R-22 equipment, is you could use R-407C and 417A to retrofit of A/C units, while for refrigeration, R-404A and 507A are available

  4. #4
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: retro fit r22 to r410a

    As long as the existing pipework is the size that is required for the new system then you will be fine with a flush...make sure you blow the lines out very well with nitrogen. Also make sure you install filter dryer and your purge nitrogen during brazing. Then when done with brazing make sure you pull a vacuum of between 250-500 microns and that it holds that with the vacuum pump turned off and everything equalized you may want to keep it above 4000 microns for a good bit to make sure you do not freeze any moisture in the system from pulling a vacuum to quick. Come back after a week of running and change the filter dryer. This may seem excessive but better to do it once then have to do it twice.

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: retro fit r22 to r410a

    WHY???????

    Ian

    What is wrong with 407??

  6. #6
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: retro fit r22 to r410a

    Is it a retro fit or a complete change out of equipment?

  7. #7
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: retro fit r22 to r410a

    hi, just doing a swap on a little split system,...weighed in endoflush and weighed it back out and blew the be jesus out of the pipe work wit ofn and gave it a vac to0 400microns so i sure it will be good..

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: retro fit r22 to r410a

    Mitsubishi has special AC with special build in filters to flush the excisting system.
    http://www.mitsubishi-aircon.co.uk/d....asp?id=152713 in the middle of the page
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2007
    Location
    Kitty Hawk, N.C.
    Age
    66
    Posts
    21
    Rep Power
    0

    Re: retro fit r22 to r410a

    If the lineset is of adequate size and is in good condition, an R-11 flush would be acceptable, IMO.
    I witness many competitors here in the states that do not even use a flush kit and simply purge with nitrogen. Many do not nitrogen sweep while brazing either. Bad decisions.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: retro fit r22 to r410a

    Flush with R11?
    We even can't buy this for many years in our country.
    The ODP's of all the refrigerants are compared to R11 and you still flush with R11?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: retro fit r22 to r410a


Similar Threads

  1. Pressure Testing for R410a
    By Pooh in forum Tools and Calculators
    Replies: 33
    Last Post: 13-08-2008, 11:41 PM
  2. R410A pressure in air conditioning
    By irwinchong80 in forum Technical Discussions
    Replies: 4
    Last Post: 06-10-2007, 07:33 PM
  3. R410A - state of art
    By MrReds in forum Refrigerants
    Replies: 2
    Last Post: 04-03-2007, 10:56 PM
  4. Detection - is it air or R410A?
    By stalker in forum Technical Speculations
    Replies: 21
    Last Post: 24-02-2007, 01:48 AM
  5. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    By DaBit in forum Technical Speculations
    Replies: 10
    Last Post: 27-11-2003, 09:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •