    mr slim



    Hello guys, just a quick question about a couple of old mr slim cassettes. A customer of ours has a very old mr slim 14Kw ish, cooling only system that has a leak in the condenser coil. We also have a previously cherished mr slim 7-8 Kw heat pump cassette that our customer wants us to fit in place of the other system. I know the original system is twice the capacity, it was grossly oversized anyway, and this other system hasn't cost us anything.We are basically doing this job for nothing, well I'll get paid for fitting it, its part of some favour/deal between my mate and the customer.
    As its not a real money making scheme, we want to keep it as cheap and quick as possible. I was wondering if we could keep the 3/4 inch suction pipe, the pipe run is only about 6-8 metres, but a pig to get to as it is in the ceiling above machinery. So i would rather not run an additional 5/8 pipe if we could get away with it.
    The newer machine is a plh3 5/8 suction, the older one was a pl6? 3/4 suction both on R22

    Andy



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: mr slim

    Hi Andy

    The 'h' in the model number refers to a heat pump.

    As you only have a relatively short suction line, oil return should not be affected to a great degree by the lower velocities within the 3/4" pipe. Providing the pipework is not, say, all vertical, I don't see any problem.

    To help with oil return though, it may be of benefit if you could replace any of the 3/4" line with 5/8" wherever possible. You will have to anyway at the connection points.

  3. #3
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: mr slim

    Hello Frank, vertical pipework is an absolute minimum, the condenser is high level on the wall outside with the connections approximately the same height as the cassette unit indoors.
    I'll go for it

    Andy

Similar Threads

  1. mr slim p8 error code
    By Krups in forum Air Conditioning
    Replies: 23
    Last Post: 17-02-2011, 07:18 PM
  2. Mr Slim problem
    By Andy AC in forum Air Conditioning
    Replies: 1
    Last Post: 12-02-2007, 10:21 PM
  3. mitsubishi mr slim master and slave
    By r600a-bang in forum Air Conditioning
    Replies: 2
    Last Post: 24-07-2006, 10:24 AM
  4. Mr Slim
    By Abe in forum Air Conditioning
    Replies: 7
    Last Post: 25-01-2006, 08:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •