Hello Marc
Have you checked all condenser fan motor thermistors they are on the control loop for the compressor circuit. If you study the drawings you will see that all eight or is it six fans have to be clear before control circuit can be enabled.
You will probably find that one of your condenser fans are seized.
The terminals for these are by the controller on the bottom terminal Blockl.
You can link these out see if this eliminates your problem.
Good Luck
-