Page 2 of 2 FirstFirst 12
Results 51 to 52 of 52
  1. #51
    superheat1's Avatar
    superheat1 Guest
    Thumbs up Re: thermal Overload
    Hello Marc
    Have you checked all condenser fan motor thermistors they are on the control loop for the compressor circuit. If you study the drawings you will see that all eight or is it six fans have to be clear before control circuit can be enabled.
    You will probably find that one of your condenser fans are seized.
    The terminals for these are by the controller on the bottom terminal Blockl.
    You can link these out see if this eliminates your problem.
    Good Luck
  2. #52
    Mar 2006
    Lancashire
    1,859
    28
    Quote Originally Posted by superheat1 View Post
    Hello Marc
    Good Luck
    Hi I had checked the fasn previouslynone of them were seized there are 8 in total. The problem was traced to faulty theristors inside the compressor.
    Marc
  1. thermal mastic
    By MOHANDAS RAVI in forum Technical Discussions
    Last Post: 04-09-2010, 04:08 PM
  2. Thermal Efficiency of Refrigeration System
    By hussain316 in forum Refrigeration Books
    Last Post: 31-07-2007, 08:59 PM
  3. Overload tripped lesson
    By rosliin in forum Domestic
    Last Post: 26-06-2006, 03:49 AM
  4. Setting Overload
    By Abe in forum Electrical
    Last Post: 06-01-2006, 01:53 PM
  5. Replies: 15
    Last Post: 24-07-2003, 08:20 PM