    Refreshing memory



    Can anyone tell me what the cfm value is for a room per square metre or where i can access a chart etc? I remember designing at college using CIBSE guidelines but that was a long time ago.
    Anyone refresh me??



  2. #2
    Join Date
    Apr 2001
    Location
    Topeka, Kansas
    Age
    76
    Posts
    16
    Rep Power
    0

    Cool CFM in a Room

    Well Reg-
    I'm sure the standards in Kansas must be different but here's what we do. For most commercial applications, we're looking for a minumum of 1.25 cfm per square foot (almost 12 cfm per square meter). In residential use, we'd like to get at least half that amount
    If I've answered the wrong question, let me know.
    Bruce H. Robinson
    bhrobin@anchor-robinson.com
    company page: www.anchor-robinson.com
    personal page: www.anchor-robinson.com/bruce01.html

  3. #3
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    You need someplace between 300 and 400 CFM per ton, depending on coil size, latent load, etc. Do a load size, convert to tons and supply the appropriate air for the load in that room.

  4. #4
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    718
    Rep Power
    23
    .......... DO A LOAD CALC..................... for your application... you're not designing on "rule of thumb" are you?

    the factor differs on application..... "Don't get me started........"


Similar Threads

  1. Mobile phone memory
    By phil68 in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 18-03-2006, 07:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •