    Burn out procedures



    Ive just fitted a rebuilt compressor 20 HP part wind which failed due to two phasing. On strip down the engineers informed me that they found lots of pink inside it and this indicates moisture.
    Not wanting to hire a crane out again and go through the same process in a couple of months ive fitted a new liquid line drier and suction burn out drier. How long should i leave the burn out in for in an ideal situation? Or should i just go back and take a ph test kit each week?



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Ideally, you want to remove the suction line filter-drier once the acid has been removed for the system. A replaceable core type filter-drier makes this easy... Simply replace the core with a suction filter element, or leave the shell empty. A Sporlan RSF-4811-T shell with an RC-4864-HH core would be correct here (assuming a 1-3/8" OD suction line).

    If the problem is you used a sealed model filter-drier in the suction line for cleanup... Actually, with a 20 ton a/c system, you would have some difficulty finding a sealed model filter-drier large enough to do this. So the Prof will assume you have a shell in the suction line.

    With the system getting some reasonable operational duty, a week of two will be plenty of time to allow the drier to do its work.
    Prof Sporlan

  3. #3
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    Reggie,

    I will suggest that you take a oil ph for the first time at one week, the second within a two week of the first one. You can go up to three tests depending on the result, on the degree of burnout on your system

    Usually i suggest a oil change after a week are two of running, especially if the oil test is marginal.


    kathleen
    Kathleen, P.eng
    www.refri-ozone.com

  4. #4
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    Is there a pH type sight glass like the moisture indicator types?

  5. #5
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Is there a pH type sight glass like the moisture indicator types?
    None the Prof is aware of. Mmmmm... must give some thought to this..
    Prof Sporlan

  6. #6
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    If you indeed invent one, can I get the first one off the line (at wholesale of course! LOL)

    Zolar

  7. #7
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    Should be possible to make one. I bet it would sell very well too. Hey prof, get Sporlan to do this and I will never buy ALCO again.

  8. #8
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    HEY!!!!!!.... Ditto, here......

    A ph/moisture combo sightglass would be "stock" on my trucks!!!!!

  9. #9
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Should be possible to make one. I bet it would sell very well too. Hey prof, get Sporlan to do this and I will never buy ALCO again.
    Alco? The Prof seems to recall that brand name....

    The Prof confirmed with his chemists that this issue had been considered a number of years ago. Apparently, finding an indicator that will change color consistently at the appropriate acid numbers, and not get itself dissolved in the refrigerant proved a bit of a problem. Might just have to get them to look at that problem once again..
    Prof Sporlan

  10. #10
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    Prof, Look in Sporlans rear veiw mirror. Alco is the company back there trying to copy all of your stuff and make it cheaper. They are doing a good job on the cheap part.

  11. #11
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    Sigh......well, maybe an indicator could be installed on the suction line near the compressor........doesn't acid give off vapours?

    Perhaps one that you could open and replace the indicator like a core-type dryer?

    How about an electronic version?

  12. #12
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    Wait a sec.........

    How about one that if the indicator is missing (dissolved) within a period of time - say less than 1 year, the tech would instantly know something's amiss (acid ate the indicator away) and do further diagnostic's?

    If it's dissolved after a year, test the system as you would regularly do and install a new indicator?

  13. #13
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    If it's dissolved after a year, test the system as you would regularly do and install a new indicator?
    LOL! And while the tech is at it, he might as well replace the compressor.
    Prof Sporlan

  14. #14
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    Prof it is coming to that point. I had a small glass chiller in a bar, 404 system. I just replaced the compressor last summer. Evap sprung a leak and contaminated the POE oil. I offered 2 prices: change oil and new compressor. Difference in my cost is $60. That is what the difference I quoted too. I had to do the same work to change the oil as change the compressor. I convinced them the new comp. was worth the difference in price.

Similar Threads

  1. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  2. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  3. Motor burn outs
    By bernard in forum Industrial Compressors
    Replies: 8
    Last Post: 25-06-2005, 11:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •