    acid oil, copeland



    hi, does someone have expierence with acid oil in airconditioning systems, which have never been opened and never had an motorfailure or water in the system. we noticed this especially with Copeland ZR310 scroll compressors, which are mounted in twin. some systems whe have changed oil and after one year with maintenance, we noticed again acid.

    regards

    octav



  2. #2
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: acid oil, copeland

    What type of oil in this compressor?
    What trademark you use the acidity test?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: acid oil, copeland

    You state that the system has never been opened but then state that you have changed the oil.

    How did you change the oil without opening the system?

    Why did you start changing the oil?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: acid oil, copeland

    The oil travels around the system, install burn out drier. Check for acid at regular intervals and change oil again and again and again until system is clear of acid .

  5. #5
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: acid oil, copeland

    Sorry remember to check pressure drop over drier and remove when system is clear of acid.

  6. #6
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: acid oil, copeland

    Quote Originally Posted by octav View Post
    hi, does someone have expierence with acid oil in airconditioning systems, which have never been opened and never had an motorfailure or water in the system. we noticed this especially with Copeland ZR310 scroll compressors, which are mounted in twin. some systems whe have changed oil and after one year with maintenance, we noticed again acid.

    regards

    octav
    Okay, so you've opened up a system that's never been opened just to change the oil.

    This is normally not done in a properly sealed system but, it seems you've found a potential problem that will eventually kill the compressor. So maybe what you've done as a preventative maintenance is a good thing.

    If acid is beginning to build in the system then you need to find the cause. I would start with the electrical supply, i.e. imbalanced voltage, power surges, improper voltage, single phasing, etc.

    From there look for a small leak in the system which would allow air and moisture to enter. Also check for overheating.

    Next clean the system properly as dirk has suggested.
    Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com

  7. #7
    Join Date
    Aug 2009
    Location
    new zealand
    Age
    57
    Posts
    44
    Rep Power
    0

    Re: acid oil, copeland

    Your acidity test may be unreliable, after more than one year of running with acid in the system the winding should have allready failed.

  8. #8
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: acid oil, copeland

    Many of the new synthetic oils are naturally very slightly acidic. A sensitive acid testing kit may pick up this acidity as a "fault". Have the oil checked by a lab against a new sample of the same oil (brand and type) it may be nothing to worry about. Also do not assume an unopened system has no moisture. Things go wrong with the best manufacturers. Ask Toyota.

  9. #9
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    235
    Rep Power
    15

    Re: acid oil, copeland

    Most probable thing that will happen is that you will keep having acidity. Many of the acids testers can be faulty. You can check the oil pH by using a "litmus paper"(don't know if this expression exists in English, sorry) that you can buy in a pharmacy. If pH is below 7, it would be recommendable to clean the circuit.

    If you don't remove that acidity 100%, you will have acidity in the system again, and so, the compressor will die sooner or later.

    You can place filters that won't remove the acids, or perform a real cleaning of the system.

    regards,

    Nando

  10. #10
    octav's Avatar
    octav Guest

    Re: acid oil, copeland

    thanks for all reply. I would also not open a proper sealed system, but some maintenace contract ask for an acid test. we renewed the acid tests to be sure we have a new proper one, with the same result. the oil is original Copeland and also renewed oil.
    I already ordered for a labo test to be sure about the quality of the oil. I will take also the suggestion about the electrical supply from Powell.

    regards

  11. #11
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: acid oil, copeland

    imho,
    The acid test needs to be chosen depending on oil type.
    All acidity tests are based on a visual estimation of change color of a test liquid.
    Wrong perusal of the instruction for the acidity test can mislead.

Similar Threads

  1. Acid in System
    By redelburg in forum Technical Speculations
    Replies: 9
    Last Post: 03-06-2010, 11:45 AM
  2. copeland scroll durability
    By Third_techtrio in forum Technical Discussions
    Replies: 16
    Last Post: 23-01-2010, 05:47 AM
  3. copeland digital scroll tech
    By Lc_shi in forum Air Conditioning
    Replies: 6
    Last Post: 27-05-2009, 12:24 AM
  4. Sourcing a modern equivalent to old USA Copeland compressor
    By weeksy in forum Industrial Compressors
    Replies: 7
    Last Post: 15-05-2009, 03:46 PM
  5. Acid cleanup
    By Larry2 in forum Heat Pumps
    Replies: 8
    Last Post: 03-06-2008, 06:36 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •