Results 1 to 14 of 14
Thread: Smelling units
    Mar 2006
    Lancashire
    1,870
    22
    Smelling units
    we keep getting called to a schools IT department where they complain of the units smelling. There are probably 8 or 9 split units in total, each in different classrooms.
    The problem is with only a select few where the teacher keeps complaing " there is a smell coming from the AC"
    The units are about 12 months old and like new. Each time we get on site, we spray coil cleaner on the indoor coils, rinse through the coils and the tray with water and then put a smelly jelly in the return air on top of the filter.
    This works for a few weeks but then we get the call again saying they are smelling.
    What causes some units to smell and not others. Is it stagnant water in the tray? Or is it something else?
    Oct 2006
    1,848
    15
    Re: Smelling units
    Quote Originally Posted by marc5180 View Post
    Two things come to mind when I read your post.
    Firstly sometimes the evap does smell when it goes from cooling to heating for a short while as it evaporates the moisture on the coil. Its not an unpleasant smell just distinctive.
    Secondley I would look to the teacher or class.
    Some people actualy do not belive in air cond and think that they are the creator of a lot of problems we have (such as sick building syndrome and such like). I'd be tempted to do the placebo test on them.
    Next time they complain go in and assure them that you have refreshed the unit without actualy doing anything.
    If they are happy at that then perhaps the problem is not the machine but the person claiming to smell the smell.
    taz.
    NC
    264
    12
    Re: Smelling units
    Is there any kind of description as to what the smell resembles? Sometimes locker rooms effect smells. Sometimes moisture left in the ducts can contribute. Is there a drain that is not normally used meaning all of the moisture has left the traps allowing sewer gas to emit from them.
    Feb 2007
    2,477
    Re: Smelling units
    Agree with all of the above.
    As you state that the units are clean, what does the condensate drain run to?
    We had it on a couple of occations where the condensate has been connected to a drain of some sort via a "normal" trap, when the trap goes dry, the unit sucs air from the drains and this smells. As a result we now use HEPWORTH traps with membranes in them.
    Mar 2006
    Lancashire
    1,870
    22
    Re: Smelling units
    Quote Originally Posted by taz24 View Post
    My first thought was this when i went into the room and couldnt smell anything. I think i should try the test next time i get called and see if it is the person claiming to smell the smell.
    Quote Originally Posted by BigJon3475 View Post
    The teachers seem to think its a musky smell, when i walk into each room i genuinely can't smell anything.
    Quote Originally Posted by The Viking View Post
    Each of the cassettes have seperate drains with a trap on that all tee off 1"1/8 drain that runs the length of the building (about 25-30m) then into a main soil stack
    NC
    264
    12
    Re: Smelling units
    I would be looking at moisture left over in ducts if your getting a musty smell. If all moisture is not removed from ducts after colling shuts off. It has a chance to sit in the duct work, drain pan, and trap. It probably resembles the musky smell when you cut your car off while it's a/c is running and then when you get back in and run the a/c at first you get a real musky high RH situation. Possible fixes would be run a delay off timer to help dry out the duct work. After cooling process is done with an evap. coil the air leaving the evap. is close to 90-95% relative humidity. When the system shuts off all that moisture is still left there to absorb into insulation and what not. I'm a residential guy so not formiluar with your situation just throwing ideas out.
    Feb 2007
    2,477
    Re: Smelling units
    So, if the trap for an individual unit dries out, then that unit would suck air from the main soil stack?
    Oct 2006
    167
    12
    Re: Smelling units
    Hello All,
    From my experience there are two types of smell that can come from a fan coil unit.
    The first is from bacteria on the heat exchangers. The smell occurs when the bacteria goes from a wet state to a dry state or vice versa. A good strong disinfectant can clear this up but you can always get the bacteria back on the coil. The bacteria comes from dirty carpets, curtains, and people (smelly armpit and all that). It can also come from beauty products like make up and perfume. (Though you would be very brave to tell a woman she is wearing cheep perfume)
    The second smell can occur if the oil used during the manufacture of the coil was not dried fully. Once the coil is made and the copper tube is compressed into the fins the entire coil is baked in the oven to completely evaporate the oil. If this process was not carried out correctly when the unit is operated in heating you will get a very strong smell. To get rid of this you need to spray the coil with a good degreaser and then run the unit in maximum heating for 24 hours.
    Marc5180 looks like you have your work cut out at the school with all those smelly teenagers
    Obi Wan
    Mar 2006
    Lancashire
    1,870
    22
    Re: Smelling units
    When i took off the cover at the side of the unit to get access to the tray ( where you put in water near the lift pump) there was a positive pressure so would it not be the same 2 inches above at the outlet of thedrain? If so then how would the smells get back to the unit?
    coilz's Avatar
    coilz Guest
    Re: Smelling units
    If you do a search for "dirty sock smell" in google you will find a good bit of info on this subject. Coil manufacturers have been dealing with this recently and for now the only solution seams to be a coil with an epoxy or electro-coating on it to resist the growth of bateria on the coil.
    It seams to happen when new units are put in place with existing ductwork. I guess the ductwork harbers the bateria and promote the growth on the coils.
    UV Lighting before and after the coils could be another option, but I'm not sure if there is any data to back this up.
    Dec 2004
    Australia
    519
    14
    Re: Smelling units
    Have had several smelly units that were installed sightly off level and water was forming in the drain pan on the opposite side to the outlet.
    Result was the remaining water in the pan would go stagnant and would smell very bad at startup.
    This condition was aggravated when you would switch to heating after long periods of cooling.
    If you get hold of the unit and physically pull it to tilt towards the drain outlet side it can sometimes cure this problem.
    Mar 2006
    Lancashire
    1,870
    22
    Re: Smelling units
    Thats a good point Temprite thanks, i'l have a look next time i get called back to site which i'm sure will be very soon.
    Marc
    Jan 2008
    ptolemaida
    37
    Re: Smelling units
    hi friend! let me ask you,in these splits did you pyt the inside drain in to the outer unit? this causes bad smells from the standing water in to the outer unit.
    Auckland
    68
    3,362
    32
    Re: Smelling units
    similar problem with similar IT geeks, resolve was fresh air make-up and issuing soap and insisting on daily showering by students. Geeks don't shower daily as they are constently cruising the NET and nothing else matters. Festering armpits and others areas.
    magoo
  1. Servicing of two portable units.
    By sortofsilver in forum Air Conditioning
    Last Post: 30-05-2010, 09:25 AM
  2. Air Cooled Mono Block Units & high Ambient
    By smpsmp45 in forum Technical Discussions
    Last Post: 11-12-2007, 06:29 AM
  3. Multiple ref. units for cold stores
    By smpsmp45 in forum Commissioning
    Last Post: 21-06-2007, 06:02 PM
  4. Mitsibishi VRV System 8 out of 10 units work
    By moondawn in forum Air Conditioning
    Last Post: 29-09-2005, 11:02 PM