    subcooling liquid line



    Hello
    Is there a improvement in systems performance, when a liquid line is clipped tightly to the suction line and both are insulated together.

    This is related to DX heatpumps using 410a gas, with capacities around 14kW, suction lines would be 22mm and liquid line 10 mm, length. of lines would be approx 15 metres. Condensing temp would be 40 degrees C and evaporating would be minus 5C

    Regards
    johnf4@mac.com



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: subcooling liquid line

    Quote Originally Posted by johnf4@mac.com View Post
    Hello
    Is there a improvement in systems performance, when a liquid line is clipped tightly to the suction line and both are insulated together.

    This is related to DX heatpumps using 410a gas, with capacities around 14kW, suction lines would be 22mm and liquid line 10 mm, length. of lines would be approx 15 metres. Condensing temp would be 40 degrees C and evaporating would be minus 5C

    Regards
    johnf4@mac.com

    Direct expansion?
    You will have to expand on where the expansion is taking place.
    Is the sytem purely a heat pump or is it reverse cycle air conditioning / heat pump.
    It depends on where the metering / expansion device is.

    Cheers taz.

  3. #3
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: subcooling liquid line

    The thought is that the small area of the liquid line in contact with the suction line will help subcool the liquid even more. I think it's called aftercooler. It's suppose to add capacity in certain cases.

  4. #4
    Join Date
    Nov 2006
    Location
    West Texas, U.S.A.
    Age
    75
    Posts
    17
    Rep Power
    0

    Re: subcooling liquid line

    Not on a heat pump, ever. That suction line will be the discharge
    line in the heat mode. The liquid line remains the liquid line.

    Probably give all kinds of problems getting the system to feed
    properly in the summer, and will flash all your liquid in the winter.

    Keep them separated on heat pumps........always.

    GF

  5. #5
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: subcooling liquid line

    Hi

    You used to be able to strap both lines together (in the old days on cooling only units) as the expansion device was in the indoor unit, and in effect you could subcool the liquid before entering the expansion device.
    Most expansion devices are now in the outdoor unit so strapping them together has no advantage.

    Cheers
    CB

  6. #6
    Join Date
    Apr 2006
    Location
    Northern Ireland
    Posts
    31
    Rep Power
    0

    Re: subcooling liquid line

    Re: sub cooling liquid and super heating suction

    Please note the Heat Pumps are geothermal units direct expansion, there are used for heating only. The evaporator is a group of 3/8 x 250 feet long copper pipe loops, buried 4 feet deep. Number of loops vary from 8 to 14 depending on size of heat pump. The loops are fed by a distributor, the expansion takes place there and is located in the loop field. There is a suction manifold which picks up the returns from the ground loops.

    I would assume the performance would be enhanced by clipping suction and liquid line together. By sub cooling liquid would give a greater refrigeration effect, super heating the suction would increase heat of the rejection, this heat is used to heat domestic hot water and underfloor heating in a brazed plate heat exchanger.

    All comments and advice appreciated.

    mac_J.

  7. #7
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: subcooling liquid line

    There is little to nothing to gain in to strap the suction and liquids pipes together on a R410A system. If it had been R404A for instance there would have been something to gain. Also to be avare of with R410A is that you get rather high discharge temperatures which is further increased with increased suction temperatures. However at -5/+40 that shouldnt be a problem anyway.

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  3. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •