    metering device sizing



    what determines the size of metering device needed for a refrigeration system?

    a. the horsepower of the compressor

    b. the Btu capacity of the evaporator

    c. the capcity of the compressor in Btu at the evaporator operating temperature

    d. the capacity of the condenser at the operating ambient temperature

    (please pick one and comment if you'd like)



  2. #2
    Join Date
    Dec 2002
    Location
    Malaysia
    Age
    59
    Posts
    86
    Rep Power
    22
    The evaporator capacity at the evaporating temperature and the calculated pressure difference between low side and high side , static losses and the friction losses in the pipes and fittings.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    I've got to go with (b)

    Frank

    Wouldn't this be better off in a "Poll" format?

  4. #4
    Join Date
    Feb 2001
    Location
    USA
    Age
    63
    Posts
    264
    Rep Power
    24
    Well hopefully you have determined the btu/h requirements for the space and product you are trying to control.... which would give you a specific evaporator rating based on the type of refrigerant you are planning on using... and then the required metering device would be based off that.
    :D
    Dean
    Subzero*psia

    Extinction is simply proof of failure to adapt.

  5. #5
    Join Date
    Feb 2001
    Location
    USA
    Age
    63
    Posts
    264
    Rep Power
    24
    I believe what you are saying here Marc is.... its a "system dependant" question..... hehehehehheh!
    :D
    Dean
    Subzero*psia

    Extinction is simply proof of failure to adapt.

  6. #6
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Amusingly, either b) or c) can be correct, depending upon the situation.

    Given a single evap, single compressor system, sizing based on compressor capacity at the design operating conditions makes sense, and we assume the evaporator is properly sized so that the compressor can operate as design conditions.

    If we have a multiple evaporator system connected to a compressor rack, and perhaps some of the evaporators being controlled with eprs, then one must rely on the evaporator rating at the desired operating condition to size the expansion device.
    Prof Sporlan

  7. #7
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    The compressor(s) shall create the refrigerant flow. And condenser, evaporator, and line sizing shall determine the operating conditions. For metering device sizing, there's the rub....
    Prof Sporlan

  8. #8
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    The rub is: the valve can't pass more ***** than the compressor can pump. If the valve passes less ***** than the compressor wants to pump, operating conditions change to make the compressor pump as much as the valve passes.

Similar Threads

  1. Piping and line sizing in lbs/min
    By Kathleen in forum Tools and Calculators
    Replies: 18
    Last Post: 29-05-2009, 03:07 PM
  2. Compressor sizing using R404a
    By PCL in forum Refrigerants
    Replies: 4
    Last Post: 14-08-2006, 11:09 PM
  3. Replies: 10
    Last Post: 20-07-2006, 10:00 PM
  4. Sizing for Australia
    By dogma in forum Fundamentals
    Replies: 5
    Last Post: 17-03-2006, 10:05 AM
  5. Metering device?
    By Apoc in forum Industrial
    Replies: 18
    Last Post: 20-07-2004, 09:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •