    Evaporator Td Correction Factor



    Most of the Evaporators are calculated at 6oC Td. When the Relative Humidity is to be raised the Td is below 6oC. Has any one got the correctyion factors for assesing the Evaporators at the various Td with R 22 refrigerant.

    I shall be grateful if some one can help me.



  2. #2
    Join Date
    Sep 2007
    Location
    New Zealand
    Age
    80
    Posts
    54
    Rep Power
    17

    Re: Evaporator Td Correction Factor

    Hi Man . There is no direct rule of thumb, but fof all conditions above freezing the performance is based on the LMTD ,(Log mean temperature difference) (T1-T2)/ Loge(Ti,T2), and the surface transfer coeficient . This can vary from below 19 watts/m2/LMTD, to >34 w/m2/LMTD. The evaporators basic design is important,air flow rate, between 1.5 to 3 meters. sec and the refrigerant supply and distribution has to be able to cope.Best to check manufactures data if you can.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporator Td Correction Factor

    Samarjit,

    If the manufacturers rating is based on TD (entering air temperature minus evaporating temperature) then you can divide the published rating by the rated TD. This gives you the basic unit rating of kW per °K of TD. Then you can simply rate the coil for other conditions by multiplying this value by the desired TD.

    You have to read the rating basis used by the manufacturer to be accurate.

    If the evaporators are rated with a refrigerant other than R-22, look at the different rating factors used for air-cooled condensers. These usually have various ratings for different refrigerants. It may give you an indication of the magnitude of the change.

    Or, ask the manufacturer for the specific rating.
    If all else fails, ask for help.


  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Thank you Mike,

    What you have stated is more on the same line as Heatcraft. I am interested in installing a plant with RH 97% without using the additional humidifiers. For this I require about 3oC Td. All the manufacturers have stated in their literatures a minimum of 6oC and was not very clear about the selection procedures.

    I hope you are back now and slightly free.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator Td Correction Factor

    I think that you have great tool for your calculations.
    Just type "coolpack software" in Google.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Evaporator Td Correction Factor

    Samarjit,
    Is this what you're looking for on page 21, right side of the page http://www.heatcraftrpd.com/resource...H-ENGM0806.pdf
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Peter 1,

    Thanks for your help. I have the manual of Heatcrafts both the soft copy as well as the hard copy. We are using only Heatcrafts Larkin Evaporators for all our projects.

    What I am interested to know as to how do I find the capacity of the Evaporator at a Td other than what is specified in the Catalogs, I guess that Mike has provided some answers. I am interested in knowing more. Maybe it is my curosity to learn at this age.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporator Td Correction Factor

    Samarjit,

    As an example: if you take an evaporator sized for a 6°K TD and operate it with a 3°K TD, then the unit capacity will be 1/2 of the capacity at the 6°K TD rating.

    To obtain the required refrigeration capacity with the 3°K TD the evaporator capacity will have to increase by a factor of 2.

    This raises the evaporating temperature assuming the air temperature is constant. By increasing the evaporator temperature, the vapor pressure difference between the coil and inside room air is also decreased. This results in higher room RH.

    Does that help?

    The one thing I think you need to be careful of is the TXV's. If a standard TXV is used for low superheat control it will control erratically if the load changes from a steady state operation.

    A balanced port TXV or EXV may provide better control.

    Also, when you operate with low TD's the amount of superheat you have for controlling the TXV is also much lower so you may need accumulators to provide protection for the compressor.

    If this was an ammonia system you would not have these problems if a flooded or liquid overfeed evaporator were used. An ammonia TXV would work as described above.
    If all else fails, ask for help.


  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator Td Correction Factor

    Quote Originally Posted by Samarjit Sen View Post


    What I am interested to know as to how do I find the capacity of the Evaporator at a Td other than what is specified in the Catalogs, I guess that Mike has provided some answers. I am interested in knowing more. Maybe it is my curosity to learn at this age.
    REMOVEhttp:REMOVE/REMOVE/tinyurl.REMOVEcom/38pu2tREMOVE

    Just use this software and insert your data, and software will calculate catalog data for you. Its free and easy to work.
    Last edited by nike123; 08-10-2007 at 10:25 PM. Reason: failed to post picture

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hello Nike 123,

    Which is the link to the software you are talking about.

  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Mike,

    Thank you for the information. This is more helpful. I propose to use EEVs for such applications.

  12. #12
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Evaporator Td Correction Factor

    Hi, Samarjit Sen

    Quote Originally Posted by Samarjit Sen View Post
    Thank you Mike,

    What you have stated is more on the same line as Heatcraft. I am interested in installing a plant with RH 97% without using the additional humidifiers. For this I require about 3oC Td. All the manufacturers have stated in their literatures a minimum of 6oC and was not very clear about the selection procedures.

    I hope you are back now and slightly free.
    Part of answer is given by US Iceman -bigger evaporator then problems with TXV, but I am afraid it will not be possible to come to such high RH without humidifiers....

    Practically it can be very expensive....and final results not good...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  13. #13
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Josip,

    I have been able to achieve upto 90% without the humidifiers. The humidifiers that I am using is adiabatic humidifiers. I have to try to get 97% without the humidifiers, but shall retain ultrasonic humidifiers for emergency and which will only start if the humidity does not increase beyond 90%.

    What is your opinion?

  14. #14
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Evaporator Td Correction Factor

    Hi, Samarjit Sen

    Quote Originally Posted by Samarjit Sen View Post
    Hi Josip,

    I have been able to achieve upto 90% without the humidifiers. The humidifiers that I am using is adiabatic humidifiers. I have to try to get 97% without the humidifiers, but shall retain ultrasonic humidifiers for emergency and which will only start if the humidity does not increase beyond 90%.

    What is your opinion?
    My opinion...I have to admit I am not an expert for food preservation in cold stores i.e. to prescribe recommended temperature and RH), but working with people doing just that I've learned that we need to have and use humidifiers to reduce product weight/moisture loss...

    Idea to have ultrasonic humidifiers is ok(at least you can spray water on the floor of cold room in case you need more moisture), but you can try without and see what will happen...of course, please, come back with final results

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  15. #15
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Dear Josip,

    Incrasing the humidity by spraying water in the floor is a process which is being followed by a lot of people. This creates hindrances in working. Further spraying water molecules by means of humidifiers makes the cardboard cartons containing the fruits etc wet and spoils the packages.

    As it is the treated water contains Sodium Chloride, which is again harmful to health. Now creating a high humidity with humidifiers the possibilities are damaging the packages and also providing sodium chloride.

    Now as far as I could think, there are two possibilities. One is to have ultrasonic humidifiers by which the sizes of the water molecules are 0.8 to 1 microns and as such instead of depositing on the floor or the product boxes they shall remain suspended in the air, In this case the water supply has to be through a RO system. The second option is to have a low Evapotaor Td and raise the RH level to 97%. This will no doubt be an expensive process, but the result will definately be better. This will involve the use of some special controls to attain a very accurate Te, uniform flow of refrigerant and a constant Evaporative Pressure.

    I will keep you informed as to the progress as I make.

    With best wishes,

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator Td Correction Factor

    Quote Originally Posted by Samarjit Sen View Post
    Hello Nike 123,

    Which is the link to the software you are talking about.
    I can't post link because I don't have 15 posts yet.
    Just type "coolpack software" in Google and first result is link to download site.

  17. #17
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    I have the CoolPack. Unfortunately it does not have the datas as required by me or what I am looking for. However thank you very much.

  18. #18
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi everybody,

    The relationship of TD and evaporator capacity is not absolutely linear. The correct procedure is : you have to find the new capacity at new evaporating temperature and new TD. When you find the correction factors and plot them you will see that the graph is not a line (is not linear).
    These correction factors can be calculated by basic refrigeration analysis taking into account the refrigerant densities at new conditions.
    By knowing the capacity at a given conditions then you can find the new capacities and then divide this new capacity to the known one to get the correction factors. You may notice in some manufacturers catalog the correction factors are greater than 1 but in some, the figures are less than one. This is why in some catalogs you have to divide the figure and in some you have to multiply the correction factors.

    I have done this for our evaporator catalogs many years ago. It is not difficult if you know what you are doing.

    Using an evaporator with 3°C TD is little bit scary. Some of the reasons are given by the others and also it would be so huge and also would cost a fortune.

    I will be in a site with four cold stores for Kiwi fruit during next week for commissioning. These are designed with 5°C TD. I will post the results here for discussion.

    Hope you get your answer.
    Cheers
    Even Einstein Asked Questions

  19. #19
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Lana,

    Thank you for your opinion and suggestion. I shall be keenly awaiting to hear from you regarding your proposed visit to the sites for the commissioning of the plants.

    I shall be happy if you could please provide me with the details.

  20. #20
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Quote Originally Posted by Samarjit Sen View Post
    Hi Lana,

    Thank you for your opinion and suggestion. I shall be keenly awaiting to hear from you regarding your proposed visit to the sites for the commissioning of the plants.

    I shall be happy if you could please provide me with the details.
    Hi Samarjit Sen,

    By all means. I will post the results on the forums.
    Hope it goes well .

    Cheers
    Even Einstein Asked Questions

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evaporator Td Correction Factor

    Quote Originally Posted by Samarjit Sen View Post
    I have the CoolPack. Unfortunately it does not have the datas as required by me or what I am looking for. However thank you very much.
    If you are not familiar with CoolPack, could you, please, post here project data? Maybe I could make calculations with CoolPack tools for you, if you send here all needed data.
    These are green numbers in input rectangles (see picture on this address: hZZZttpZ:Z/Z/tinyZurl.cZom/2ZZen9bm ).

    Remove Z from address!

  22. #22
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Thank you nike123,

    I have got what I wanted. I am now awaiting to hear about the results from Lana.

  23. #23
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Everybody,

    I have just came back from the site. This site has 4 cold rooms for Kiwi fruit. Each room has two compressors but the number of evaporators varies.
    The biggest room has one 40HP compressor with three evaporators, also one 35 HP compressor with two evaporators. The 40HP system is designed with TDe=5°C but the 35HP system is designed with TDe=8°C (because of economic reasons the owner asked me to do this). Anyway, I did not have enough time to adjust the TEVs so I have to visit the site again. I measured -0.5°C room temperature with 92%RH. We have 45m of pipe run on this system but there is no oil return problem. There are no products in these rooms so we have to wait and see what happens when they are loaded.
    There are some installation problems because the contractor did not follow my instructions but now I can do nothing because it is done.

    Commissioning a system is relatively easy if you have designed the system because you are sure about the components and their design data.

    So far I am happy with these systems but the real result is when they are loaded.
    I will keep you informed.

    I have attached some photos for you.

    Cheers
    Attached Images Attached Images
    Last edited by lana; 19-10-2007 at 02:49 PM.
    Even Einstein Asked Questions

  24. #24
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hello Lana,

    It appears that you have done a good job. The actual status will only be available with the rooms being loaded.

    In the projects that we do the rooms are as large as the one done by you. The refrigeration loads are at the maximum 38 kw. Further what we are doing that we are having individual Evaporators with each Condensing Units.

    I would be very keen to learn more after your next visit to the site.

  25. #25
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporator Td Correction Factor

    Quote Originally Posted by lana
    Commissioning a system is relatively easy if you have designed the system because you are sure about the components and their design data.
    That is absolutely true. I just started up a highly modified ammonia liquid overfeed system last week. Start up only took two days. The biggest problem found was the controls contractor still needs to do some more work. Otherwise the system ran great.

    Nice job lana!
    If all else fails, ask for help.


  26. #26
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Samarjit Sen and US Iceman,

    Thank you. I will keep you informed when the rooms are loaded. Hope it goes well.

    Cheers
    Even Einstein Asked Questions

  27. #27
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi everybody,

    As promised I would like to inform you how the project went. I just came back from the site and they started to load the Kiwi into the cold rooms.
    First let me explain something which I did for the first time. I ordered a system to an electronic company to monitor temperature and relative humidity inside the cold room. The difference is this system can accommodate up to 32 sensors in a room. This system works like this : you choose how many sensors you want to put in the room, then you input their relative co-ordinates (relative to the door) into the panel, then on the screen you can see the sensors as a dot. The system reads the temp. and RH for each sensor and shows them on another panel. (the picture is attached).
    We installed this system in one room with 8 sensors. These sensors cover the perimeter of the room. With this system you can monitor the temp and RH differences in one room which would be caused be incorrect loading.
    I got between 90 and 98% RH with 0°C all around the room. I must mention that there is no humidifier or wet floor.

    As you can see from the pictures, the loading is not finished yet but so far everything goes as designed.

    So as I explained many times in this forums, high RH can be achieved by correct evaporator design.

    Cheers
    Attached Images Attached Images
    Even Einstein Asked Questions

  28. #28
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Evaporator Td Correction Factor

    Indeed, VERY nice job Lana.
    Are these Profroid evaporators?
    They look anyhow like Profroid.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  29. #29
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi Peter,
    Thanks a lot.

    No, they are manufactured by my own company.
    They are home made.

    Cheers
    Even Einstein Asked Questions

  30. #30
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Evaporator Td Correction Factor

    Wawwwwwwwwwwwwww
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  31. #31
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporator Td Correction Factor

    Quote Originally Posted by lana
    The 40HP system is designed with TDe=5°C but the 35HP system is designed with TDe=8°C (because of economic reasons the owner asked me to do this).
    Hi lana, which system is holding the RH?

    Quote Originally Posted by lana
    I got between 90 and 98% RH with 0°C all around the room. I must mention that there is no humidifier or wet floor.
    Also, was the variation in RH due to any particular reason? The reason I am asking is I'm trying to define the actual RH range for the specific TDe and if this was constant during any time or associated operation.

    Thanks.
    If all else fails, ask for help.


  32. #32
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hi US Iceman,

    The design of two systems for this room is done according to the kg/day loading which was assumed initially. Now they can not load that much product into the room therefore, only 40HP system is working and it is enough to pull-down the temp. (the reason they can not load that much is because of shortage of fork lift and personnel).
    So up till now only 40HP system with TD=5°C holds the RH. When the room is fully loaded, I will visit the site and will bring the 35HP system into operation and see what happens.

    The variation of RH is normal except for one sensor which shows the highest of all (98%). This sensor is the nearest to the door and product was loaded directly beneath it. I assume that these are the reasons for the high reading. I might change this sensor next time to see what happens (of course if I can go into the room after the loading).

    The other sensors were showing from 90 to 93% which is acceptable. First I suspected the readings and I put my Testo hand held Hygrometer into the room but it registered the same value for RH.

    I hope I explained it well.
    Cheers
    Even Einstein Asked Questions

  33. #33
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Evaporator Td Correction Factor

    Hello Everyone,

    I was away for quite some time and visited one of my sites. The Pre Cooling Rooms and the Cold Storages are being loaded with Pomegranates, where the required Room Temp. is 4oC and a RH of 90%. I found that without using the humidifiers these conditions were being maintained. As in within a few months the party would be loading Grapes, just out of curosity, I had the temperature brought down to -1oC Room Temperature and found the RH has gone upto 98% and was being maintained.

    I have disconnected the humdifiers as they are not required.

    As Lana says that we can attain the high humidity with the Evaporators and without any additional humidifiers if the system design is correct.

    The temperature and the RH is uniform throughout the Room and I did not install any controls such as EEV or CPR.

  34. #34
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporator Td Correction Factor

    I'm seeing a consensus starting to form!

    The interesting point brought up by all of this is; if the system is designed properly, it should produce the desired results.
    If all else fails, ask for help.


Similar Threads

  1. R-22 to R-502 Capacity correction factor?
    By The MG Pony in forum Refrigerants
    Replies: 8
    Last Post: 23-04-2007, 04:04 AM
  2. Heat Rejection Factor
    By nh3simman in forum Fundamentals
    Replies: 18
    Last Post: 20-04-2007, 02:40 PM
  3. Unit cooler rating factor
    By nh3simman in forum Fundamentals
    Replies: 4
    Last Post: 17-03-2007, 02:58 PM
  4. power factor correction
    By marley821 in forum Technical Discussions
    Replies: 4
    Last Post: 06-05-2006, 08:29 PM
  5. Looking for "K" factor and "U" factor tables
    By mayot in forum Fundamentals
    Replies: 1
    Last Post: 03-02-2006, 09:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •