    carrier chiller desuperheater fot hot water



    HI sir
    There's one 30HRZ-280 carrier recip chiilers need to add desuperheaters to recover heat for hot water.
    I consider to apply stainless PHE for this application. I've not done this job before and not sure if there's any risk for the existing chiller. The process should be : let off the refrigerants --cut off the discharge line--connect the PHE to it --leakage check --reevacumm the system ---charge --confirm the operation is OK.
    The chiller capacity is 930kW and will recover the 2/4 circuits. It's a rather big system. I'm not sure how long time to take to do the vacumm.

    Anybody can give me some clues?thx!

    regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: carrier chiller desuperheater fot hot water

    Vacuming should be done until it's, on a analog vacuum gauge, between 0 and 5 mbar, depending on the surrounding temperature and left standing for at least 2 hours. If there's more then 30 kg of refrigirant in it, you'll have to vacuum until 10 mbar and then broken with ofn to 0,05 bar and then vacumed until 0-5 mbar. Then again standing test of at least two hours.

    Do keep in mind, you'll have to keep the crankcase heaters on while vacuming, otherwise you won't get all the refrigirant out off the oil.

    Use ofn while brazing, that way you will keep everything clean and also flush out some resudial refrigirant from the oil.

    Vacuming the system takes as long as is needed until the system is between 0 and 5 mbar. It can be 2 hours or two days, depending on how large the system is.

    Good Luck!

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: carrier chiller desuperheater fot hot water

    Quote Originally Posted by Lc_shi View Post
    ..... The process should be : let off the refrigerants --cut off the discharge line--connect the PHE to it --leakage check --reevacumm the system ---charge --confirm the operation is OK.....
    I do hope that you mean to recover the refrigerant and not let it go to the atmosphere.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    AmmoniaMan's Avatar
    AmmoniaMan Guest

    Re: carrier chiller desuperheater fot hot water

    Well, what happens with hot water when cooling load goes down?

  5. #5
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: carrier chiller desuperheater fot hot water

    If you are using a stainless steel PHE make sure you use the right grade of stainless and you will also need to check the hot water for Chlorites, should not be more then 200ppm from memory as they will eat into the stainless and cause leaks.

  6. #6
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: carrier chiller desuperheater fot hot water

    I have seen this setup designed and built at the factory on both Carrier and Trane recip chillers. They rarely performed as designed. Just shooting from the hip and adding a PFHX IMO is asking for problems.

    They tended to go thru compressors. The compressor failures happened if it was the factory servicing the chillers or independents. By the time you added up all the additional expenses, I don't see how they ever recieved any type of a payback. JMHO

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: carrier chiller desuperheater fot hot water

    Hi sirs
    Thanks for your kind suggestions and serious doubt about it.
    I'll recover the refrigerant by using a split ac outside unit(I've no any recovery machine at hand). The selected PHE has 0.3bar pressure loss which has little affect to the chiller.
    It's no problem if the retrofit process is well controlled.
    Recover heat to hot water is better than to disperse the heat to the atmosphere.
    The system contains 68kg R22. Is there any good way to recover it? welcome your input.

    thx and regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: carrier chiller desuperheater fot hot water

    Hi, Lc_shi

    Quote Originally Posted by Lc_shi
    Recover heat to hot water is better than to disperse the heat to the atmosphere.
    I am always to utilize recuperation of heat from process ....better then to throw it to mother nature....

    ....if not for us payback will be for our children...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: carrier chiller desuperheater fot hot water

    If the hot water is potable, you will need a special vented wall design exchanger to meet the required codes of prevent cross contamination of the water with refrigerant.

    Also, in this type application, you will still require a full sized condenser to reject the heat if you are not removing any with the heat recovery condenser.

    Ken

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  2. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  3. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Replies: 7
    Last Post: 18-01-2007, 10:06 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •