    Re: Frost elimination inside a cold storage room

    Hi Josip and Spoc, the frost formation is mainly in the middle of the panel not in the seams. The frost is like snow over the door and 2m away on the ceiling, also in the corners of the room. The frost in the evaporator is light and its defrosted every 8 hrs by hot gas, the fans have a 3 minute delay.

  2. #2
    Join Date
    Nov 2006
    Location
    Lancashire,UK
    Age
    47
    Posts
    12
    Rep Power
    0

    Re: Frost elimination inside a cold storage room

    What size is the room? I have a feeling that it is only small an poss a Porkka or equiv.
    You get what you pay for.

    8 hours for hot gas is not enough and I would reccomend little and often. I usually set them for every 4 hours with a duration of 10 - 12 mins and a termination of about 8 - 10 deg C but this does depend on the size of room, equipment and where the Evap probe is sited asumming it is electronic.
    Last edited by Spoc; 06-10-2007 at 01:45 PM. Reason: was a bit hasty and blunt before!

  3. #3
    Join Date
    Oct 2007
    Location
    Guatemala
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: Frost elimination inside a cold storage room

    Hi Spoc. The room dimensions are 30m long x 16m wide x 7m height. It has two recirculated evaporators FRICK, model SCA-463TL operating with a temperature difference of 10F.
    I’ll reschedule the defrost times at your suggestions.

  4. #4
    Join Date
    Sep 2007
    Location
    New Zealand
    Age
    80
    Posts
    54
    Rep Power
    17

    Re: Frost elimination inside a cold storage room

    Quote Originally Posted by Frio1 View Post
    Hi Josip and Spoc, the frost formation is mainly in the middle of the panel not in the seams. The frost is like snow over the door and 2m away on the ceiling, also in the corners of the room. The frost in the evaporator is light and its defrosted every 8 hrs by hot gas, the fans have a 3 minute delay.
    Hi Folks
    Where access to a room at -20 C is direct from an anti room at +25C/ 85% rh the laws of physics will cause quite rapid air exchanging with the resulting snow generation . The only fully successful method of ensuring a frost free space in the cold store is to condition the air in the load in load out area, but if the complex has not been built to accommodate this a retro fit is expensive . This topic has been responded to else where in this forum describing Desiccant Wheel technology through to refrigerated coils . If the provision of suitable conditioning of the load out area is not an option then the access door opening closing cycles will have to be addressed. I agree with US Iceman the location of the room evaporators and air flow have a big effect on the generation of the snow. If the evaporators are above the door and the air flow parallel to the air being induced the entrainment effect will make it worse. Snow build up in the corners of the wall where the door and on the ceiling 2 metres away is characteristic of the "S" flow of air through door ways which is fully explained by ASHRAE. These are the points where the velocity of the warm air , caused but the buoyancy effect is slowed down sufficiently to freeze and deposit the "snow". Extra defrosts will not necessarily solve the problem either. Here in NZ our local MAF come down hard on us in meat export stores if there is an ice build up. Most new stores are designed with an "ELA"; Environmental Load-out Area", with refrigerated air conditioning systems installed. If the design and installation is correct the initial extra cost is offset by a reduced operating cost of the cold store for its effective life.

  5. #5
    Join Date
    Oct 2007
    Location
    Guatemala
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: Frost elimination inside a cold storage room

    Hi John Hunter:

    Thanks for the comments. Your right with the snow pattern inside the room, and yes, I agree that the best way to avoid this problem is conditioned the hall, but at this moment there’s not an economical and practical way to supply treated air to it. Few years ago I read on some internet place, but I misplace the address, that installing fans facing the corners inside the room can eliminate the problem by sublimation of the frost. You are familiar with it?

Similar Threads

  1. Cold Room Design - minus 25deg C
    By vijay_study in forum Fundamentals
    Replies: 34
    Last Post: 11-11-2009, 07:12 AM
  2. Cold storage - Onions room
    By Kevin Yeo in forum Fundamentals
    Replies: 31
    Last Post: 14-02-2008, 03:42 PM
  3. Frost Formation in Cold Rooms
    By Samarjit Sen in forum Technical Speculations
    Replies: 21
    Last Post: 04-08-2007, 05:19 PM
  4. troubleshoot a two door storage room
    By duraid in forum Fundamentals
    Replies: 7
    Last Post: 13-12-2006, 06:57 AM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •