    R410A pressure in air conditioning



    hi, anyone familar with R410A. For air conditioning system, R22 pressure in discharge is 250psi and suction in 67psi. But for R410A pressure will be more higher that R22. So what pressure is normal for air-conditioning systems. Besides that normal R22 compressor can replace with R410A refrigerant!



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: R410A pressure in air conditioning

    You don't have a pressure temperature chart?
    If you do, air cons on r22 are normally at the pressures you listed, because that's the designed saturation temperatures, r410a systems with be at the same saturation temperatures (indoor temp -20k, outdoor temp ~ +20k)
    so an r22 air con running at 67psi LP (4 degrees C) and 250psi HP (~48 deg. C) would be running at the same temps on r410a, which equals 118psi LP and 412psi HP.
    No, you can't use an r22 compressor because of the higher pressures and r410a needs a different oil.
    R407c is a more direct replacement of r22, still needs a different oil, but would run at 57psi LP and 245psi HP

  3. #3
    Join Date
    May 2007
    Location
    NC
    Posts
    264
    Rep Power
    17

    Re: R410A pressure in air conditioning

    Quote Originally Posted by irwinchong80 View Post
    hi, anyone familar with R410A. For air conditioning system, R22 pressure in discharge is 250psi and suction in 67psi. But for R410A pressure will be more higher that R22. So what pressure is normal for air-conditioning systems. Besides that normal R22 compressor can replace with R410A refrigerant!
    http://www.lennoxcommercial.com/res/...10a/frame1.htm

  4. #4
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: R410A pressure in air conditioning

    That was a good link, I even took the test and passed yippeee

  5. #5
    Join Date
    Aug 2006
    Location
    in my house
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: R410A pressure in air conditioning

    good link thanks

    simon

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    By DaBit in forum Technical Speculations
    Replies: 10
    Last Post: 27-11-2003, 10:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •