    Daikin FXSQ100M8



    hi guys was commissioning this indoor unit today testing pump ect.... Found myself taking off the supply ducting to poor water into the drip tray to make the pump run...

    Is there an easier way to test the pump? maybe from the board, as when doing alot of units this would get slightly frustrating?

    also how much water should it take until the float is made and the pump runs? approx?



  2. #2
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Daikin FXSQ100M8


  3. #3
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Daikin FXSQ100M8

    thanks for link to site will come in handy! as for testing the pump was trying to find out how you guys go about testing internal pumps?

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin FXSQ100M8

    The easiest I found is with a Garden Sprayer. Just fill with water, pump up the pressure and spray the coil until the pump starts.

    It might be tricky on ducted units but it's normally a small hole somewhere and the lance for a garden sprayer are less than 1/2"

  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Daikin FXSQ100M8

    i know most mitsubishi unit have a small side plate that can be removed in order to pour water in,i mainly use a 5L spray doc with a small lenght of 3/8 hose on for test internal and external
    Paul


    "KEEP IT COOL"

  6. #6
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Daikin FXSQ100M8

    Haven't the daikin ducted units got a removable black plastic plug on the side of the unit by the drain outlet?
    you may be able to run the pump from the controller, however I am not familiar with Daikins these days, I know you can on a MHI. Anyway that wouldn't help you if you couldn't get the water into it in the first place

    Andy

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin FXSQ100M8

    Quote Originally Posted by Andy AC View Post
    Haven't the daikin ducted units got a removable black plastic plug on the side of the unit by the drain outlet?
    Spot on Andy - that's exactly what the inspection cover is for. I'd put at least 2 litres into the unit to test the lift pump and/or any subsequent tank pump.

    One of the biggest call backs on A/C is for condensate removal problems. Special care at install stage will reap rewards later.

  8. #8
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin FXSQ100M8

    Quote Originally Posted by SkyWalker View Post
    hi guys was commissioning this indoor unit today testing pump ect.... Found myself taking off the supply ducting to poor water into the drip tray to make the pump run...

    Is there an easier way to test the pump? maybe from the board, as when doing alot of units this would get slightly frustrating?

    also how much water should it take until the float is made and the pump runs? approx?
    Hello Skywalker,

    See the attached JPEG from the installation manual for the FXSQ-M indoor units.
    There is a hole just below the drain outlet for you to pour water in.

    If you just want to run the lift pump then put the indoor unit in the “Fan Only” mode, then press the “TEST” button repeatedly until you see “TEST” displayed on the remote controller, then press the ON button.
    The Fan and the lift pump will run for half an hour.

    Otherwise use the FORCE.

    Obi Wan
    Attached Images Attached Images

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •