    White Foam During Unloading



    Hi,

    I am curious to know, why liquid line sight glass start to bubble with kind of white foam during unlading of 1 bank of semi hermetic compressor.

    Compressor is 40 HP Copeland compressor. Operating conditions are 25/110F.

    Thanks in advance.



  2. #2
    Join Date
    May 2007
    Location
    NC
    Posts
    264
    Rep Power
    17

    Re: White Foam During Unloading

    Sounds like liquid slugging from being overcharged or having liquid return back through the compressor.

  3. #3
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: White Foam During Unloading

    Thanks BigJon,

    The foam or bubbles goes away as soon as system unloading is over.

    And the Superheat at the compressor is approx 10 deg.

    Do U still think, if this is the case of slugging?

  4. #4
    Join Date
    May 2007
    Location
    NC
    Posts
    264
    Rep Power
    17

    Re: White Foam During Unloading

    Quote Originally Posted by jwasir View Post
    Thanks BigJon,

    The foam or bubbles goes away as soon as system unloading is over.

    And the Superheat at the compressor is approx 10 deg.

    Do U still think, if this is the case of slugging?

    What's the amp draw like during startup?

  5. #5
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: White Foam During Unloading

    Quote Originally Posted by jwasir View Post
    Hi,

    I am curious to know, why liquid line sight glass start to bubble with kind of white foam during unlading of 1 bank of semi hermetic compressor.Thanks in advance.
    If it is the LIQUID LINE Sight Glass foaming,that is not an indication of slugging.
    My first thought would be that this is a because of a sudden drop of Head Pressure when the compressor unloads.
    You can verify this with your guages.
    Last edited by NH3LVR; 30-09-2007 at 06:32 AM. Reason: spelling

  6. #6
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    395
    Rep Power
    18

    Re: White Foam During Unloading

    NH3LVR
    that sounds about right also the suction pressure will come up reducing the pressure differential across the metering device thus reducing flow. Without more information it is difficult to give more advice.

    Ian

  7. #7
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25

    Re: White Foam During Unloading

    This is most likely the liquid in the liquid line reaching its flash point, try increasing your subcooling so when you unload the affect is less - although I think its got to do with mass flow rates too and line sizing, I only ever see it on single systems with one liquid line, racks with headers don't tend to see this.
    ...and she said "give it to me you big fridgie"

  8. #8
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: White Foam During Unloading

    Thanks to all for the nice explanation.

  9. #9
    Join Date
    Sep 2007
    Location
    New Zealand
    Age
    79
    Posts
    54
    Rep Power
    17

    Re: White Foam During Unloading

    Quote Originally Posted by jwasir View Post
    Hi,

    I am curious to know, why liquid line sight glass start to bubble with kind of white foam during unlading of 1 bank of semi hermetic compressor.

    Compressor is 40 HP Copeland compressor. Operating conditions are 25/110F.

    Thanks in advance.
    Hi jwasir.
    What is the refrigerant R22??. Could be oil problem .
    JH

  10. #10
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: White Foam During Unloading

    Quote Originally Posted by John Hunter View Post
    Hi jwasir.
    What is the refrigerant R22??. Could be oil problem .
    JH
    The Refrigerant is R-22.

    I tried to increase the sub cooling , as advised by one member.

    This didn't solved the problem completely.

    The system is complete with Low ambient package and Hot gas By-pass.

    The head pressure is maintained at 225 PSI by dumping hot gas in the receiver and also the HG by-pass is always on to maintain the min required suction pressure of 55 PSI.

    Now while charging, LL sight glass get almost clear but again starts to bubble in few minutes.

    The subcooling before the receiver is approx 30F and after the receiver is 10F.

    The comp. is 40 HP copeland with 2 unloaders. When 2 bank unloads the sight glass gets worst and less than half glass can be seen with kind of white fluid flowing in it.

    When both cylinders are loaded, the sight glass gets nice and clear.

    Does the system needs more ref. How much?

  11. #11
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    263
    Rep Power
    18

    Re: White Foam During Unloading

    hi jwair, best way to charge your system is make sure ther is a good load on evaporator,possibly do a cuircut at a time.........also you bubbling problem sounds like you cant really help as you are dumping from the recever as you say which is liquid and by opening the by pass and exposing the high side to this pressure drop, will cause some flashing to take place...it acts like a pmv by the sounds of it

    rgrds phil

  12. #12
    Join Date
    Apr 2007
    Location
    lancashire england
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: White Foam During Unloading

    turn the sight glass round so u cant see it then go to the pub

  13. #13
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25

    Re: White Foam During Unloading

    Quote Originally Posted by wineman View Post
    turn the sight glass round so u cant see it then go to the pub
    I like your style
    ...and she said "give it to me you big fridgie"

Similar Threads

  1. White Oil
    By The captain in forum Refrigerants
    Replies: 14
    Last Post: 28-10-2008, 02:02 PM
  2. White Goods
    By bernard in forum Domestic
    Replies: 2
    Last Post: 14-04-2007, 08:52 PM
  3. Polyurethane Foam Insulation
    By Samarjit Sen in forum Technical Speculations
    Replies: 1
    Last Post: 20-08-2006, 07:03 PM
  4. Loading / Unloading Control Question...
    By Bluenoser337 in forum Industrial Compressors
    Replies: 31
    Last Post: 02-05-2006, 06:03 PM
  5. white goods web site
    By ksvinod in forum Computers & the Internet
    Replies: 4
    Last Post: 06-09-2005, 08:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •