    Trane Rtaa 213 Air Cooled Liquid Chiller



    I Have Been Working On The Above Chiller Here In Abuja, Nigeria For The Past One Month Below Is The Problem I Have With The System.this Sytem Has 2 Circuits With 1 Compressor(rotory) Each On Circuit A & B Respectively. The Comprssor On Circuit A Is Working Ok, While That Of Circuit B Runs For About 2 Minutes Then It Trips On Fault Message As Follows:"low Oil Flow". I Have Replaced The Oil Filter Several Times. It Seems The Oil In The System Is Ok. Please Advise Me What To Do Next.besr Regards,ahamed Kyana



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    What's the ambiant out there at the moment?

    Have you checked the condensing temperature sensor and the oil temperature sensor to see if they are correct?

    Check if the pressure on the display corresponds with that off the gauge!

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    What type of compressor is on there?

    Does it have an internal or external oilfilter?

  4. #4
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Hi ahmedkyana,
    Is your UCM CHILLER module 1U1 or UCP 2.
    Ckt B - Low oil flow - CMR - Compressor Energized - code a - Possible Causes - Differential oil pressure switch remained open for a single period of more than 20 seconds. Check this out.

  5. #5
    Join Date
    May 2006
    Location
    new york city
    Posts
    75
    Rep Power
    18

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    I have had the same problem on a RTAA 125 air cooled chiller.. The service tech found it to be a defective oil temperature switch.. Resetting the unit using the stop start switch on the display had the same results as you are experiencing. After stopping the unit and shutting the Main Power completely to the unit we were able to restart until the new part was obtained. Hope it works for you

  6. #6
    Join Date
    Sep 2007
    Location
    NIGERIA
    Posts
    8
    Rep Power
    0

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Hi Abdulazman,
    The ucm chiller model ucp2. What do you think will cause the Differential oil pressure switch remained open for a single period of more than 20 seconds.?

    Best regards


    Ahmed kyana

  7. #7
    Join Date
    Sep 2007
    Location
    NIGERIA
    Posts
    8
    Rep Power
    0

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Hi sanderh,

    The compressor is Trane Heli rotor and has an external oil filter.Thank you for your concern.


    Best regards,



    AHAMED KYANA

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Then there's a oil differntial pressure switch in the terminal box.

    If you've changed the filter, did you open the valves and before that did you evacuate the filter?

    Have you checked that there's enough oil in the system?

    And once again, what was the ambiant temperature?

  9. #9
    Join Date
    Sep 2007
    Location
    NIGERIA
    Posts
    8
    Rep Power
    0

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Hi Sanderh,

    Thank you for the effort.

    Yes there is an oil differntial pressure switch in the terminal box.

    As I 've changed the filter,I did opened the valves and then evacuated the filter.

    There is enough oil in the system.

    The average ambiant temperature in Abuja Nigeria is between 35 - 45 deg C.

    Best regards,



    AHAMED KYANA

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    If you've evacuated it well and checked there's enough oil, my gues is the oil differential switch, but it can also be the solenoid valve in the oil line on the other side of the screw compressor. The switch measures oil before the oil filter and after the solenoid valve!

  11. #11
    Join Date
    Sep 2007
    Location
    NIGERIA
    Posts
    8
    Rep Power
    0

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Hi sanderh,

    Thank you for the response.I shall place an order for new oil filters,oil pressure switch and oil line solenoid valve and do it all over again. I will keep you posted on the development.

    Best regards,



    AHAMED KYANA
    MOBILE:*********
    Last edited by frank; 01-10-2007 at 08:46 PM. Reason: Please keep phone numbers for the PM system

  12. #12
    YAC's Avatar
    YAC Guest

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    I HAVE A RTAA 217 AND IN DISPLAY OF A UCM "CIRCUIT 2 IS TOO HOT" what i can do ? i change a probe and reset the UCM.Please Advise Me What To Do Next or send me an document of RTAA 217

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    Quote Originally Posted by YAC View Post
    I HAVE A RTAA 217 AND IN DISPLAY OF A UCM "CIRCUIT 2 IS TOO HOT" what i can do ? i change a probe and reset the UCM.Please Advise Me What To Do Next or send me an document of RTAA 217
    First, try to post this as new question in this or other appropriate forum. Then, explain your big problem wit more than few shortcuts and 1 sentence.

  14. #14
    Join Date
    May 2008
    Location
    Auckland
    Age
    44
    Posts
    7
    Rep Power
    0

    Re: Trane Rtaa 213 Air Cooled Liquid Chiller

    All trane literature (IOM'S) are available from trane.com, They provide useful information required to maintain and carry out basic servicing tasks as per manufactures specs.

Similar Threads

  1. Trane Air Cooled Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 26
    Last Post: 11-04-2007, 08:30 PM
  2. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  3. trane chiller
    By ric in forum Air Conditioning
    Replies: 3
    Last Post: 14-09-2006, 08:03 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •