    Carrier ducted unit



    Hello guys, got a problem with a large packaged all in one ducted a/c system (condenser ducted). System has been running best part of 2 years no problem until yesterday - water pissing out of middle of unit- condenser fan section. Both drains are clear, I have trapped them as well but it didn't make any difference. Water seems to make its way out of the condenser tray and into the fan section and leaks out through the casing and through ceiling down onto very annoyed lady sat at desk below
    Unfortunately the unit is a pig to get at and the shop has the worst ceiling grid in the world and most of it will have to be removed to sensibly get to anything. Has anybody got any suggestions/advise before I start ripping the shop apart monday morning.

    Andy



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Carrier ducted unit

    I think the best thing to do is get up there and have a good look,id be checking:

    drip pan
    filters (if its a pig to get too have they been done)
    motor/belts
    all covers on right

    then pouring water in to see just what is going on
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Aug 2007
    Location
    england
    Age
    40
    Posts
    4
    Rep Power
    0

    Re: Carrier ducted unit

    I have had this problem before.
    It was due to the condensor fans sucking the condensate into areas that arent protected by a drip tray.
    I had to adjust the fan speed to allow maximum efficiency but minimum leaking.
    As this unit was being stripped out we did not investigate further.

  4. #4
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Carrier ducted unit

    Air velocity of the system at the return?

  5. #5
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Carrier ducted unit

    Got back to it today finally found cause of the problem -drip tray, wasn't airflow or duct problems like we first thought. Well its not actually a proper tray, just a couple of bits of angled sheet metal spot welded to the floor of the unit and siliconed up afterwards - crappy design. Problem is that the water is leaking into 2 areas, the condenser fan area and also through the spot welds in the floor into the outer casing.
    I don't want to drill out the spot welds because A) I can't get to most of them, access is a nightmare, I'm dangling off the top of my stepladder and B) I don't want to risk causing more problems later on such as rust etc.
    Can anybody think of a product that is water resistant that I could either spray or paint over the existing seals. I can't get a silicone gun in to the offending area so it would need to be spray or paint.
    I have called Carrier and left messages with them but so far they haven't called back with any suggestions so any additional help/advise muchly appreciated.
    What would you guys do?

    Andy

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Carrier ducted unit

    If you can get to it, i've bodged things up with flat roof repair paint before or gutter sealant.

  7. #7
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Carrier ducted unit

    Quote Originally Posted by monkey spanners View Post
    If you can get to it, i've bodged things up with flat roof repair paint before or gutter sealant.
    we had some really reallly old carrier 4 way cassettes with leaking drip pan that where no long available,one coat of that and hey lasted two years before being ripped out
    Paul


    "KEEP IT COOL"

  8. #8
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Carrier ducted unit

    "Foster® 40-60™ Drip Pan Coating
    Foster® 40-60™ Drip Pan Coating has excellent long-term resistance against the detrimental effects of harmful fungus, algae, and bacteria, and will not support their growth on the coating’s surface. It will also provide vibration dampening. Foster 40-60 has the water resistance and low water vapor permeance normally found only in solvent-based coatings. It can be used in high humidity or wet environments. It will greatly retard moisture vapor penetration and inhibit corrosion of metal surfaces.
    Foster 40-60 may be placed in service after a minimum of 96 hours dry time. It dries forming a strong bond to galvanized steel, aluminum, or mild steel surfaces.
    Foster 40-60 contains no asbestos, lead, mercury or mercury compounds."

    http://www.fosterproducts.com/defaul...etails&pid=185

    I have used Fosters for other reasons and they make a good product.

  9. #9
    Join Date
    Oct 2007
    Location
    Scotland
    Posts
    12
    Rep Power
    0

    Re: Carrier ducted unit

    Andy,

    What is the model number of the unit? I maybe able to help.

    Regards

    Ian

  10. #10
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Carrier ducted unit

    Hello Imac, the model number is 50YZ04879 the other number on it, probably serial number is 074E00642.
    If you can help, I'd love to hear from you.

    Andy

  11. #11
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Carrier ducted unit

    Black bituminous paint is the stuff to use! Makes a right mess everywhere and stinks, but two coats of it has cured me problem

    Andy

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. Ducted unit in chippy
    By Climateman in forum Air Conditioning
    Replies: 19
    Last Post: 15-05-2007, 12:18 AM
  3. Daiking ducted unit water leak
    By marc5180 in forum Air Conditioning
    Replies: 19
    Last Post: 03-10-2006, 10:09 AM
  4. Phoenix Carrier Reefer Unit Trouble
    By razorback76 in forum Trouble Shooting
    Replies: 4
    Last Post: 11-07-2006, 07:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •