    Self contained ice cream freezer , unexplained pressures ?



    I am working on a small self contained ice cream freezer and it seems to have a high low side pressure and a low high side pressure.

    300 kpa low side
    500 kpa high side
    R134a

    unit is not cycling
    it has a full bore of liquid to the metering device.

    any ideas.


    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  2. #2
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Self contained ice cream freezer , unexplained pressures ?

    What's the amperage draw as opposed to RLA? or even better what is it compared to the compressors performance chart?

  3. #3
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Self contained ice cream freezer , unexplained pressures ?

    Have not checked the amp draw as yet.



    but as a guess i would say it would not be too high as the thermal overload does not trip.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  4. #4
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Self contained ice cream freezer , unexplained pressures ?

    Okay heres what you need to do check superheat, subcooling, Outside temp, amperage draw and the pressures all at the same time. When you get those then we can make an informed decision till then we would all be guessing. Someone answered you on the other site by the way.

  5. #5
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Self contained ice cream freezer , unexplained pressures ?

    Cheers , thanks for the help.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  6. #6
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Self contained ice cream freezer , unexplained pressures ?

    comp inefficient, valves shot likely.
    ...and she said "give it to me you big fridgie"

  7. #7
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Self contained ice cream freezer , unexplained pressures ?

    I had a few minutes of time to check all the system operating temps and pressures.


    The amp draw on running is 1.60 , which does seem to be in the range it should be.


    The manufacturer states it should have a RLA of 1.90 at an evaporating temp of 10 degrees celcius which is my 313 kpa.


    The charge that is in it should give me an evaporating temp of -25 degrees celcius which equates to a current draw of 1.22 , so the amp draw is slightly high in this aspect.



    condenser SC was 0.8 degrees celcius

    evap SH was 16.8 degrees celcius

    ambient was 24 degrees celcius
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  8. #8
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Self contained ice cream freezer , unexplained pressures ?

    Hi

    I assume you have 16.8 degrees of superheat or is 16.8degrees the temperature you measured at the evap outlet??

    If you have 16.8 degrees of superheat then i would assume the expansion device is either shut down or blocked. If it is blocked then that would explain the low discharge pressure.
    Whats the cabinet temperature.
    i assume it is a gylcol filled bunker chiller.

    I believe you are evaporating at around +9deg C.?



    CB

  9. #9
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Self contained ice cream freezer , unexplained pressures ?

    Finally did the comp change , and all went well , only thing now is the system runs in a vacuum at - 50 kpa and the case is not cooling.


    The operation of the system has totally reversed itself , when the comp was changed the whole system was flushed out to prevent blockage and there was an abnormal amount of oil in the tube.

    N2 was used while brazing.


    System has a fine bore cap tube , so now i suspect waxy oil is logging around the system.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

Similar Threads

  1. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM
  2. Ice cream display & Sale freezer
    By Rayin in forum Commercial
    Replies: 5
    Last Post: 27-07-2007, 08:15 AM
  3. R290, walls ice cream freezer
    By Andy W in forum Commercial
    Replies: 1
    Last Post: 22-06-2007, 07:49 PM
  4. Freezer efficiency questions
    By M_Q in forum Fundamentals
    Replies: 8
    Last Post: 20-03-2007, 04:38 PM
  5. Ice cream freezed with sound
    By Peter_1 in forum New Technologies
    Replies: 3
    Last Post: 11-05-2006, 02:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •