    please help urgent



    I have fitted a mitsubishi heavy industries SRK 40-HG has been working fine however it will not switch onto the heat mode.

    check pressures low pressure is around 1.7 to 20bar when the comp running,and in the heat mode the 3/8 pipe work is getting very hot however the the blower unit will not blow air out warm air if i switch it to cool mode then the blower unit blows perfect nice and cool canyone please help
    thanks
    richie

    trickie999@yahoo.com



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: please help urgent

    What is the pressure then? 1.7 to 2.0 ? And what refrigirant?

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: please help urgent

    In heating mode the fan will not start until the coil get warm enough (mitsu=40 degrees C IIRC).
    As you state that the pipes are getting warm and you have seen a pressure reading of 20bar (but I suspect you connected the gauge line to the valve on the outdoor unit, if so, when the unit is in heating you are looking at a discharge pressure, not suction), I suspect the system doesn't read the correct coil temp.

    I recommend that you check the resistance of the coil thermistor and that the thermistor is located where it belong.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: please help urgent

    How is this "Urgent Please Help" at 10pm on a Friday night in the UK?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: please help urgent

    Hey Brian.

    Give the guy a break, it's cold out there tonight

  6. #6
    Join Date
    Sep 2007
    Location
    uk
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: please help urgent

    sorry guys yes it was bloody cold last night anyway using r410a can olny test on the low pressure side and gauge was reading 1.7 to 2.0 bar only using about 3 meters of pipe work its has been fine all summer on the cold but now winter here lol well it bloddy feels like it no heat can anyone help cheers

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: please help urgent

    1.7barg - 2.0barg on R410a = SOG?? most probably

  8. #8
    Join Date
    Sep 2007
    Location
    uk
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: please help urgent

    sorry new to this and probaly out of my depth but sog??

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: please help urgent

    Short Of Gas

  10. #10
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: please help urgent

    1- When it's running, what's the temperature of the larger pipe between the units?
    2-When it's running, what's the temperature of the smaller pipe between the units?
    3- Assuming that the answer to q1 is >50 degrees C, what is the resistance of the coil thermistor?

  11. #11
    Join Date
    Sep 2007
    Location
    uk
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: please help urgent

    hi viking thats for all your help any chance i could give you a call think it would be easier
    im on Please use the PM service for sending numbers - Frank
    cheers
    richie
    Last edited by frank; 30-09-2007 at 08:43 PM.

  12. #12
    Join Date
    Sep 2007
    Location
    uk
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: please help urgent

    ran the system up on heat mode and checked on the outdoor unit on union and have 15 bar pressure the pipe temp is around 50c however havent broken into the unit yet as i have only had this unit 4 months so dont no if it will void the warrenty tried to find out what pressure i should have but have no info and tried to test the high pressure side and the is no test point should the low pressure side have higher pressure than 15 bar???? could this be as simple as SOG??
    thanks for you helpvery new to this iam car mechanic do air con on the cars but the spilt system on house easier to install but when they go wrong help

  13. #13
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: please help urgent

    OK,
    50 Degrees C on the pipe and the indoor fan doesn't start?

    Time to call in a professional.

    The fault is in the controls but if you aren't used to trouble shooting A/C controls then it's better left to someone who is.

  14. #14
    Join Date
    Sep 2007
    Location
    uk
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: please help urgent

    the indoor unit still under warrenty bought from hrp online guess i need to speak to them maybe its an exchanged indoor unit some people say its just short of gas on this site why ???

  15. #15
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: please help urgent

    some people say its just short of gas on this site why ???
    Because you said you had a reading of 1.5 - 2.0 bar. With 410A this will give you an evaporating temp of between -25 to -30°c, which would make a nice deep freezer.

  16. #16
    Join Date
    Sep 2007
    Location
    uk
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: please help urgent

    right i see best i give hrp a phone on monday and see if they will exchange the indoor unit for another

  17. #17
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: please help urgent

    trickie999
    I doubt very much if they will change it as part of their warranty requirement is that the unit is installed and commissioned by a competant person, from your comments it would appear as though you may not meet the criteria. I suggest you call in somebody who knows what they are doing before you contact HRP.

    Ian
    PS. why do we need control on the people allowed to buy and install kit???

  18. #18
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: please help urgent

    Hopefully you havn't been using your car gauges on it as the pag oil in them may cause all sorts of nasties....

Similar Threads

  1. urgent
    By A_Ahed in forum Trouble Shooting
    Replies: 6
    Last Post: 31-07-2007, 09:45 AM
  2. urgent
    By Dimitris in forum Trouble Shooting
    Replies: 7
    Last Post: 18-10-2006, 05:55 AM
  3. Urgent G Fault Codes Needed
    By botrous in forum Trouble Shooting
    Replies: 10
    Last Post: 08-08-2005, 08:13 PM
  4. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •