    Question Weird pipe runs



    System install,

    hi guys one thing i have noticed when going on any course, manafactures specify pipe max/min runs, max/min height diff of evap/cond, max distance from first refnet ect ect, but i have never seen them specify certain conditions to be avoided......

    for instance say you had a really weird and wacky pipe run lots of ups and downs 45' 90' ect i mean REALLY out of the ordinary,

    what im trying to ask is, are there any situations you guys try to avoid when installing pipe work or are you completely oblivious as long as pipe run doesnt exeed max (taking into acount bends ect)



  2. #2
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Weird pipe runs

    That's kinda a loaded question IMO. If it has "lot's of bends and 45º, 90º"...." Then most likely you'll be well above the normally recommended 2-3 psi pressure drop. So it would depend specifically on how many 45's 90's and how long the line set was weather or not you use risers or long radius couplings instead of reg. couplings. The manufacture doesn't have every equation out their to give you every scenario. You have to use your best judgment and go by the min/max the manufacturer can recommend.

  3. #3
    Join Date
    Jan 2006
    Location
    Surrey
    Posts
    26
    Rep Power
    0

    Re: Weird pipe runs

    Manufacturers frequently state a maximum 'equivalent' pipe length which would include for bends etc.

  4. #4
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Weird pipe runs

    thats what i do just wonederd what you guys thought on the situation!

  5. #5
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Weird pipe runs

    Probably contact manufacturer and get them involved with anything outside the "box"

  6. #6
    Join Date
    Sep 2007
    Location
    u.k.
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: Weird pipe runs

    could someone explain to me what would happen if you exceed the recomended pressure drop and what exactly long radiius couplings involve..thanks

  7. #7
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    17

    Re: Weird pipe runs

    http://www.refrig.com/Ref%20Pip%2002.pdf


    This will at least give you some ideas.
    Attached Files Attached Files

  8. #8
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    72
    Rep Power
    18

    Re: Weird pipe runs

    Most manufactureres have a max pipe run and max equivalent pipe run. The equivalent run assumes a few bends are included but figures are never given. On VRF or VRV systems it is not uncommon for the systems to compensate for long runs with high pressure drops by altering the compressor speed. The unit calculates the pressure drop during during an oil recovery cycle the outdoor unit knows the back pressure so therefore the evaperator temperature, by asking the indoor units what the real evap temperature is the unit can determine the pressure drop. To see this in action go to 2 similar systems (same manufacturer) and measure the back pressure units with long runs will have lower back pressures than those with short runs, this overcomes the pressure drop.
    splits dont know the real back pressure so they have to either guess or some have a long short pipe run switch which is a crude way of doing the same. Non Inverter units just struggle on with reduced capacity

    If you want more explanation come to our vrf service course go to www.mylg.co.uk and click training for details

    hope to see you all soon.

Similar Threads

  1. Pipe runs
    By SPR in forum Air Conditioning
    Replies: 11
    Last Post: 07-04-2009, 07:28 PM
  2. extra length v pipe size v additional charge
    By misterfixit in forum Air Conditioning
    Replies: 18
    Last Post: 03-01-2007, 07:57 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •