    location of the expansion valve



    We have a blast freezer coil ( R 404A) & the circuit is as shown. What is the best way of putitng up the expansion valve. Logically it sould be horizontal?
    Attached Files Attached Files



  2. #2
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: location of the expansion valve

    Hi

    Normally the coil manufacturers would put a pipe extension from the liquid distributor, connect into that.
    If not, the liquid distributor should normally face vertically up or down, not horizontally side ways, if liquid is feed to the distributor horizontally liquid would start to feed the lower distribution lines first rather than equally to all distriution lines, if it is fitted vertically up or down liquid will feed all distribution lines equally.

    CB

  3. #3
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: location of the expansion valve

    Thanks for the correct view on this. & that too very fast

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: location of the expansion valve

    On DX, I would normally use a down feed on the distributor and a coil outlet on the bottom.

    You can use up feed on the distributor.

    ken

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: location of the expansion valve

    An Expansion Valve can be fitted in any direction. From the attachment sent by you, the Blast Freezer Coil is of FrigaBohn make and has multi circuit. This means that there is going to be a distributor. The distributor has an orifice inside, which ensures uniform mixing and flow of vapour and liquid to all the circuits. Please study the Bulletin 10.9 of Sporlan.

    The fixing of TEV totally depends on the space arrangement and available. The distance from the TEV to the distributor should not exceed 24" and preferrably there should not be any bend immediately after the TEV.

  6. #6
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: location of the expansion valve

    The coil is from BAP , Spain .ANyway many thanks for the details

Similar Threads

  1. Expansion Valve Selection
    By raviperumal in forum Technical Speculations
    Replies: 12
    Last Post: 17-02-2010, 09:58 AM
  2. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  3. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  4. pressure drop between expansion valve and distributor
    By aygul in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2004, 09:47 AM
  5. Oversizing EXV electronic expansion valve
    By aygul in forum Technical Discussions
    Replies: 5
    Last Post: 20-11-2003, 01:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •