Results 1 to 15 of 15
    Mar 2007
    INDIA
    42
    31
    High discharge temperature
    we had purchased the scroll compressor from Danfoss. It is worked well for two years.
    Now the Head temperature is increasing gradually and trips in temperature.
    It gives very high noise also.
    The application is chiller plant
    Evaporating temp 10'C
    Condensing Temp 45'C
    What could be the probable cause for this problem?
    Kindly help me to understand the issue.
    Best regards.
    ravi perumal
    Apr 2007
    SOUTHAFRICA
    43
    26
    Re: High discharge temperature
    check the condenser eg: fans, brittle condenser,and decrease superheat ,hope it helps.
    Oct 2001
    Nottingham UK
    5,668
    If it's been running fine for 2 years and the discharge pressure is increasing then the problem leads toward a lack of heat rejection.
    Check the efficiency of the fans and the cleanliness of the condenser coil - and look for any recent additions of nearby plant or buildings that could be affecting the flow of air over the condenser
    Mar 2006
    Greece
    34
    Based on what you say, I'm afraid the compressor needs to be changed. Usually when a scroll compressor makes that sound and heats up, it means that it has been damaged from lack of lubrication due to working at excessively high pressure and temp, as well as very low superheat (return of liquid.)
    kpntreal's Avatar
    kpntreal Guest
    Have you had a possible recent phase change?
    You are aware that the three phase scroll is direstionallly sensitive?
    REEFER-TEK's Avatar
    REEFER-TEK Guest
    I agree with dimtris,
    If you hear it make abnormal sounds, the damage is done, this is probably what is causing the high compressor temperature, When you repalced two years ago did you determine why it failed then? Most scrolls require a liquid injection or quench valve in effort to control compreesor temperature. if this valve is not working properly or the sense bulb is not installed and wrapped you will lose a compreesor again.
    tHis is just my opinion.
    Regards R-T
    Oct 2007
    Not Sure?
    I would before you change anything, Check the power and the amp draw. Resistance in the windings and put a voltage monitor on it. Damaged windings cause heat, heat trip units off.
    Seriously! What was that guy thinking.
    Pentane rocks!
    sohail's Avatar
    sohail Guest
    I also agree with dimitris,the compressor oil level must be checked and the condeser for short cycling of the discharge air back to inlet head pressures increase due to choked condenser .
    Apr 2006
    Torquay
    59
    130
    If the discharge temperature is high I would check that the superheat is not too high. If the TEV is not letting enough refrigerant through it can cause high discharge temperature, but then you would see a low suction pressure.
    Tampa, Florida U.S.A
    590
    raviperumal,
    Did you get it fixed and what was the end story?
    Just curious
    Regards R-T
    malaysia
    159
    raviperumal,
    1] u should re-consider the SDT. check with your local weather condiions.
    malaysia
    159
    raviperumal,
    2] check your condensing equipment & capacity.
    3] check cooling vs liquid level.
    Jun 2005
    Canada
    15
    Hi Ravi,
    It is your moral duty to let the forum participants to be informed what you did to resolve the issue.Don't afraid whether you did right or wrong.It can be a learning for others.
    Thanks,
    Kothri
    Aug 2001
    Havant, Hampshire, UK
    12
    Just a quick thought, I recently went to service a chiller unit with scroll compressors and found one of the four compressors running quite happily, if a little noisy, on only two of the three phases. The problem was traced to the soft start on the unit.
    Feb 2008
    Las Vegas, NV
    67
    330
    I just noticed how old this post was. Nevermind.
  1. Compressor loading, cooling, and range of operation.
  2. fun quiz
    By Brian23 in forum New to RE
    Last Post: 02-10-2007, 10:18 PM
  3. Saturated Discharge Temperature
    By nh3simman in forum Fundamentals
    Last Post: 02-05-2007, 06:36 AM
  4. Replies: 1
    Last Post: 03-04-2006, 09:18 AM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Last Post: 20-05-2003, 12:27 AM