Thread: vacuum in a recovery cylinder?
23-09-2007, 07:21 PM #1
i hope this question isnt as dumb as it sounds, but hear goes,,,
i have a brand new recovery cylinder, and i pulled a deep vacuum in it. now im working on a sandwhich cooler and i find a leak in the service valve. i tried replacing the core and it still leaks so i set up to evacuate the system for repair.
the nameplate states that it holds 11 oz of mp39. when i go to recover the refrigerant, i end up with 1.5 oz in my recovery cylinder.
which brings me to my question...
it is my understanding that if you have a cylinder with "only" refrigerant in it, it will pressurize to the correct pressure for that refrigerant at that ambient temp. why is it that when i hook my gauges, it still reads a vacuum?
thanks a bunch,
mike
23-09-2007, 08:25 PM #2
Re: vacuum in a recovery cylinder?
How big is the recycle cilinder?
11 oz is 311 gram, so on a cylinder that can hold say 28 kg that is not enough to brake the vacuum!Last edited by Lowrider; 23-09-2007 at 08:26 PM. Reason: calculation
23-09-2007, 08:54 PM #3
You need enough refrigerant to have liquid refrigerant in the cylinder to get an acurate reading.
23-09-2007, 09:02 PM #4
its a standard sized 30lb cylinder. how much refrigerant would you guess it would take to bring it up to the right pressure at 70 deg f?
thanks
mike
23-09-2007, 09:17 PM #5
Much more then you have in the sandwich cooler!
23-09-2007, 11:01 PM #6
How much air is in the cylinder that was in your manifold tubes?
24-09-2007, 09:38 PM #7
The formula to calculate the amount is:
p*V=n*R*T
p= pressure in Pa (N/m2)
V= volume in m3
n= amount of gas in mol
R= gasconstant (8,314472 Jk-1mol-1)
T= absolute Temperature in K
Let me know what you came up with!
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
Vacuum test
By Peter_1 in forum FundamentalsReplies: 15Last Post: 13-10-2006, 09:04 PM -
Recovery and vacuum equipment
By Larry2 in forum FundamentalsReplies: 2Last Post: 19-07-2006, 12:16 AM -
Can I leave a system in a vacuum overnite?
By kengineering in forum Technical DiscussionsReplies: 15Last Post: 17-05-2006, 03:03 PM -
problems with ice slurry production by spraying water in a vacuum chamber
By goodluck99 in forum Trouble ShootingReplies: 6Last Post: 16-04-2006, 01:27 AM