    We have a kitchen deepfreezer onboard controlled by an elliwell ID974.
    We cleaned it out and manually defrosted it and when we started it up again the compressor started running but the fan did not, so the temperature in the freezer didn't come down.
    When I disabled the evaporator probe by changing the parameter H42 to 'no' the fan started running and the temperature started coming down.
    When it reached normal working temperatures again, I changed the parameter back to 'yes' and the fan kept on turning and everything kept on working fine.
    But a few hours later it went in defrost and the letters 'def' appeared in the display and stayed there.
    The temperature stayed ok but the only way to get rid of the 'def' was by switching the refrigerator off and on again.
    Does anybody have an idea what could be the reason of this phenomena.
    Danny
    Re: elliwell ID974 defrost problems
    The Eliwell ID974 has some 40 instructions; it’s easy to get lost, frustrated and generally fed-up when it doesn't appear to work!
    There are two instruction FSt & FAd which together will hold off the fan until the coil reaches a certain temperature. If say, FSt was set for 5°C and FAd was set for 2°C, the fans will come on when the coil temperature reaches
    5 – 2 = 3°C.
    Another instruction FCO, will cycle the fans with the compressor during cooling.
    The display in defrost is controlled by instruction ddL.
    If ddL is set for “2” then the display will show deF when the defrost starts and continue to show deF until the air falls below the setpoint temperature.
    Full instructions for ID974 and other controllers here: http://www.frostechnic.com/service.htm
    Hope this helps.
    Italy
    Sirs,
    you can download all eliwell literature on Invensyscontrolsuerope.com website under Eliwell brand. Refrigeration controllers like ID974 are under digifrost controller. For any help you can contact
    techsuppeliwell@invensyscontrols.com
    regards
    cuepower64's Avatar
    cuepower64 Guest
    The ID974 DEF display will keep displaying until the controller setpoint is reached. As for the fans I would check that the fan off temperature parameter is not set too low, as if this is set too low the fans will not energise until the temperature drops back down to this setting due to the temperature rise on defrost. Also I dare say you have checked this but also check the fan delay time as both of these will hold the fan off after a defrost. I hope this helps!!! cuepower64
    Quote Originally Posted by boksida@hotmail View Post
    Danny
    Belgrade
    47
    10
    There is another thing that could hold the fans. Dripping time (dT) It is used to hold fans until remaining water drops turns into ice so they cant be blown off of the evap.
    Check that, too.
    4,706
    Thumbs up Re: elliwell ID974 defrost problems
    Boksida.
    I think the link you recieved from mambro 01 is corrupted.
    Please follow the link below for the relevant pdf for the ellwel ID Range including the manual for a ID974 and a ID974LX. The instruction manual link is at the bottom of the page.
    http://www.invensyscontrolseurope.co...DigifrostLine/
    malaysia
    159
    boksida,
    could you check on your temperature sensor probe/s?
    you should find somthing there.
    Devon
    73
    8
    I agree with hendry, had same problem, changed the evap probe. All OK (Prefer LAE )
    Volos, Greece
    I Had many times the same problems , sometimes the def probe can stop the fans and can be damaged without probe alarm,
    malaysia
    159
    Quote Originally Posted by Mazdamike View Post
    thank you for your concurrence.
    sometimes, i need to be a bit more adventurous in order to complete the entrusted task/job.
    no doubt, it may seem to be a simple alarm ...
    i do check the complete electrical and electronic system to eliminate any nuisance.
    anyway, good luck in case you have similar problem/s.
    BEAR IN MIND NOT ANY TWO PROBLEMS ARE THE SAME.
    Feb 2008
    stevenage england chav central
    44
    hello well to start off these controllers are easy once you get to know the patterns and the things you need to look for as someone said check the evp probe and temperature reading within the controller i am sure it is a function on this controller then check and make sure the probe is attached to the evp that could be another problem sometimes they fall off or get disloged, check evp cut in time sometimes its on a time basis or a temp basis depending on the settings within the controller and last of all check the gas charge maybe there is not enough refrigerant flooding the evp to insure that the fan comes on within the set parameters i hope this helps.
    declan
    armyeng1's Avatar
    armyeng1 Guest
    I have an elliwell ID974 Controller with LED display showing the compressor off, but the compressor continues to cool anyways and the fan does not stop. I have the SET to 2C and the Dif to 2C everything appears ok, both NTC probes are new. Any ideas?
    Dec 2009
    dublin
    14
    if u have a solenid check to see if its passing,if there is no solenid check if your controller is still sending power to compressor when its not calling 4 it
    Oct 2008
    New Zealand
    33
    Quote Originally Posted by armyeng1 View Post
    relay locked on. replace controller.
    Adelaide , Australia
    192
    How do I put Elliwell ID974 - onto defrost ?
    60% of the time it works everytime.
    Feb 2008
    adelaide sth.oz
    1,015
    hit the bugger timbo
    May 2005
    newbury
    44
    13
    Hold down top left button to defrost
    192
    Quote Originally Posted by lowcool View Post
    PDF arrived from Elliwell tech support impressive it has all the info , but i dont know how to attach it ?
    192
    Talking Re: elliwell ID974 defrost problems
    Quote Originally Posted by mambro_01 View Post
    Sirs,
    regards
    Thanks for the email address they sent me exactly what I needed in a PDF
  1. Elliwell digital controller
    By chenkang in forum Electrical
    Last Post: 25-09-2009, 11:36 AM
  2. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Last Post: 13-08-2007, 11:25 PM
  3. Freezer Room Defrost
    By Samarjit Sen in forum Commissioning
    Last Post: 21-06-2007, 06:16 AM
  4. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Last Post: 08-03-2005, 07:50 PM
  5. Oil return problems
    By Peter_1 in forum Industrial
    Last Post: 23-08-2004, 11:30 PM